If 0% of input range, square rooted out wil be 0%
If 25%of input range, square rooted out wil be 50% 12mA
If 50% input range, square rooted out wil be 70.7% 15.31mA
If 75% input range, square rooted out wil be 86.6% 17.8 mA
If 100% input range, square rooted out wil be 100% 20mA
Can someone explain how these calculations are made?
Re: Input Range Calculations
06/08/2011 10:26 PM
This sounds like a differential pressure flow meter. The flow is proportional to the square root of the pressure difference.
06/08/2011 10:40 PM
example please
06/09/2011 2:08 AM
Here is a sample correlation table for DP (differential pressure) of 0-60 with Q (flow) of 0-200.
main = output of DP transducer (input to further processing)
f = fraction of DP range
√f = converted fraction
maout = milliamp signal to indicate flow
Q = calculated flow
DP--main---f------√f---maout--Q
00---04--0.00--0.000--04.0--0
15---08--0.25--0.500--12.0--100
30---12--0.50--0.707--15.3--141
45---16--0.75--0.866--17.8--173
60---20--1.00--1.000--20.0--200