06/08/2011 10:57 PM

Dear CR4 users,

We have two 500KVA diesel generators as back up power, Our major load is thyristor load. For this type of load generators are provided with PMG as pilot exciter. My question is what is the necessity of providing PMG? Is there any relation between harmonics and PMG?

__________________
key questions why, what & how - just think
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Member

Join Date: May 2011
Posts: 8
#1

Re: PMG exciter in generator

06/09/2011 2:31 AM

Hello,

No.. As per my knowledge, There is no such relation between harmonics and PMG( Permanent Magnet Generator) it is an Exciter of the main generator which produces the residual flux at starting of the Generator

Register to Reply
Associate

Join Date: May 2010
Location: NC, USA
Posts: 34
Good Answers: 1
#2

Re: PMG Exciter in Generator

06/10/2011 9:48 AM

My understanding of the PMG was to help the generator recover quickly from the impact of large loads (eg the starting of a large motor normally draws the generator down for a few seconds, a PMG is meant to reduce that amount of time that the generator is at low voltage). I've been known to be wrong before and welcome corrections.

Chris

__________________
Chris
Register to Reply
3
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#3

Re: PMG Exciter in Generator

06/10/2011 12:49 PM

The PMG is not alone. It provides the Voltage Regulator with a steady Independent power that it will use to vary the excitation of the Pilot exciter, which in turn will provide the variable current to the Main Field.

Normally, this power is taken from the Main Generator Stator windings and, therefore, will depend a lot on what is going on on the load side:

- If harmonics are present, they will probably affect the outcome of the AVR,

- If a huge demand (relative to the size of the Alternator Capacity) is made by the load, the voltage output can be depressed for a very short time or for a not-so-short time(?). This will affect the supply to the AVR. This in turn can create a snow ball (or chain reaction) that will further depress the voltage output and so on until there might not be any remanent magnetisme to restart the chain reaction in the opposite direction.This is a rare occurence but can happen and did happen ...

- A PMG will allow the alternator to provide the required Short circuit or Fault current no matter how big is the load or the fault as well as make the excitation circuit free from any harmonics or parasitic waves due to the load.

- This setup is costlier but has these advantages if required.

Register to Reply Good Answer (Score 3)
Register to Reply 3 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Cbrunner (1); LAA_Lucke (1); Mahanteshy (1)

Previous in Forum: Low Voltage Spark Gap   Next in Forum: Data Centre Continuous Cooling

Advertisement