Anonymous Poster #1

Pipe Test

06/10/2011 12:37 AM

dear sir

I'm a mechanical engineer from Baghdad and I have I want to test the HVAC water pipes of the building

the head is 40 m

the designer is the same of the one of Dubai said you must calculate by this manner( 4 bar of the static head+ 4 bar of the pump pressure) * 1.5

it is mean the test pressure be 12 bar for 24 hours

I think this is no sense because according to physics the pressure is equal every point in the close system

thank you

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: pipe test

06/10/2011 12:44 AM

The pressure is not the same everywhere in the system. At lower points, the pressure is higher on account of vertical head. In a flowing system, upstream pressure is higher than downstream pressure on account of "friction" losses. The designer is correct in principle, but the relevant pressures may differ from 4 bar, depending on the system design.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#2

Re: Pipe Test

06/11/2011 12:38 AM

If the chilled water pipe system is to be tested before commissioning it should be tested as per the relevant professional codes. Generally it is recommended to pressurize the piping network app 1.5 times the design pressure and allow it for certain time. Observe for any reduction in pressure. Log the details. To calculate the system pressure you need to use proper formulas and HVAC handbooks .

Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#3

Re: Pipe Test

06/11/2011 8:27 AM

I'm neither a piping nor an HVAC guy, so let me ask:

  • (Incidental: I guess the water we're talking about is what's known as chilled water?)
  • I'm assuming the 40 meters of static head is because the building (or the part of it served by this system) is 40 meters tall (or extends 40 meters above the location of the pump for the system)? (This then represents a static head of 4 bar, because 1 meter of water ~= 0.1 bar.)
  • The system is closed (as you say). When the pump is running, is it intended (or designed) so that the chilled water at the top of the building is 4 bar?

If so, then the total pressure (static + dynamic from the pump) at the top of the pipe system is 4 bar, and at the bottom of the (40 meter tall) pipe system is 8 bar, and thus, if you are required to test at 1.5 x the system design pressure, you need to test at 12 bar (as measured at the bottom of the system).

If you're testing with water, when you measure 12 bar at the bottom of the system, you'll measure 8 bar at the top of the system. If you're testing with air, when you measure 12 bar at the bottom of the system, you'll also measure 12 bar at the top of the system.

Reply Score 1 for Good Answer
Reply to Forum Thread 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

mrswamy (1); rhkramer (1); Tornado (1)

Previous in Forum: Burning Calories vs Work Performed   Next in Forum: How to Take Seeds from Vegetable
You might be interested in: Bar Code Software, Bar Code Cards, Bar Code Scanners

Advertisement