Performance of Motor With Soft Starter And Fluid Coupling

06/10/2011 2:20 AM

A DOL starting motor 160 KW, 400 V driving Agitator through reduction gear and fluid coupling used in mines and mineral industry working satisfactory.

What would be effect on performance on driven Agitator and motor if same equipment (Motor-Agitator-Reduction gear-Fluid coupling) started using Soft-starter.

The use of soft starter is explored to reduce DG set rating for emergency starting of same agitators for expansion project of plant.

Pl. share your experience

__________________
When was last time you did something for first time.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Performance of Motor with Soft starter and fluid coupling

06/10/2011 4:58 AM

If your going to use a soft start why not simplify the system and get rid of the fluid coupling?

It's one less thing to go wrong. I can't see the point in having both.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#2
In reply to #1

Re: Performance of Motor with Soft starter and fluid coupling

06/10/2011 5:24 AM

The equipment is ordered with fluid coupling.

As motor size is big it is having impact on DG sizing. To reduce DG size this option is exploerd.

The equipment supplier is not confident about performance on equipment with fluid coulping and soft starter together.

Also function of both are not identical when compared with respect to starting and running characteristic of driven equipment.

__________________
When was last time you did something for first time.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3
In reply to #2

Re: Performance of Motor with Soft starter and fluid coupling

06/10/2011 5:39 AM

If the soft start has a relatively short ramp up time to control the peak loading on the generator the fluid coupling will pick up as normal.

One system I've worked on was from the 1930's it had a 150HP slip ring motor an a magnetic clutch driving a fan, you could hardly tell it was starting up

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#4

Re: Performance of Motor With Soft Starter And Fluid Coupling

06/10/2011 10:04 AM

It would depend on the start-up torque against speed curve and inertia of the machine-train. It is ideal, if you can take the operating fluid away from the coupling during motor starting, then restore it with motor at normal speed. Have you asked the makers if they have experience with your problem?

Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#5
In reply to #4

Re: Performance of Motor With Soft Starter And Fluid Coupling

06/10/2011 10:21 AM

I agree with your statement that It would depend be function of start-up torque against speed curve and inertia of the machine-train.

As motor size is small the fluid coupling shall be of simple construction without provision of taking fluid during starting.

The manufacturer of equipment has give no satisfactory reply and have no experience with such arrangement i.e. Soft Starter+Motor + fluid coupling + Agitator.

Any one who have worked with similar arrangement? Pl. reply

__________________
When was last time you did something for first time.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: Performance of Motor With Soft Starter And Fluid Coupling

06/10/2011 10:52 AM

It's done all the time. Despite what the fluid coupling people say about it providing soft starting, it's a MECHANICAL soft start, not an electrical one. A Solid State Soft Starter would technically be capable of both functions, but if, as in your case, the FC is integral it's kind of a waste to duplicate the capabilities. All you really need now is a Reduced Voltage Starter of any sort for the generator.

I absolutely HATE Star-Delta starting, I think it's a cheat: neither soft nor reduced voltage and certainly not benign. Don't go that way, you will regret it later. But a better method of reducing the effects of starting current on a DG than a Solid State Soft Starter is actually a Reduced Voltage Autotransformer (RVAT) starter. The transformer action further reduces the starting current drawn from the line by the transformer ratio, which helps the DG, where as in an RVSS the starting current is the same as the line current. It's a subtle difference and generally I don't use RVATs because they don't really provide the same MECHANICAL soft starting benefits as an RVSS. But in this case the FC is taking care of that. I would use an RVAT starter then; simpler and easier to set up in a retrofit. It may be physically much larger though, and that's sometimes an issue. In that case, go with an RVSS.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#7

Re: Performance of Motor With Soft Starter And Fluid Coupling

06/10/2011 12:05 PM

If you were to install a soft start, given one of the benefits of fluid couplings such as you have here, I would not remove the fluid clutch and replace it with a hard and fast mechanical coupling.

One of the aspects of fluid clutches is that they have the ability to "absorb" based on the shearing action inherent in a such a coupling, sudden shock loads that present to the mechanical system. That is one of the reasons they are used in agitator drives and larger centrifuge based systems.

By removing the fluid coupling, if you were to do so, you remove some of the systems ability to absorb sudden shocks and introduce another failure mode to the system.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#8

Re: Performance of Motor With Soft Starter And Fluid Coupling

06/10/2011 3:18 PM

Since I posted question on CR4, I have checked net and have come across Soft starter sizing program from ABB PROSOFT3.0 and various product catalog of fluid coupling.

From those inputs It can be concluded that addition of Soft starter in equipment train would further help in smoothening starting stress imposed by motor on equipment train.

During starting of motor as driven equipment is at stand still total energy is desipated in fluid coupling. As mechanical load accelerated this loss reduces and finaly equipment shall come to full speed.

With introduction of soft starter the torque generated by motor would be less when compared to DOL starting, resulting in less power to be absorbed by fluid coupling.

Overall effect on equipment train is expected to be

  1. Motor subjected to lower starting stress due to Soft starter
  2. Coupling subjected to less severe service.
  3. Probably more no. of starting per hours for equipment train.
__________________
When was last time you did something for first time.
Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (1); Happy singh (3); JRaef (1); North of 60 (1); TonyS (2)

Previous in Forum: Earth Strip Calculation   Next in Forum: Solar Power Generation

Advertisement