Earth Strip Calculation

06/10/2011 1:15 AM

How to calculate the size of earth strip ,wheathre it is copper,al. Some consider based on type of load (inductive, capacitive) and some consider in comer breaker amps of a particular panel .Can u get me a formula that can be used for all the above requirments

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator
Engineering Fields - Power Engineering - Power Engineering Passion Engineering Fields - Electrical Engineering - Engineering Passion India - Member - New Member

Join Date: Mar 2011
Location: Noida, (U.P.), India.
Posts: 99
Good Answers: 6
#1

Re: Earth Strip calculation

06/10/2011 5:48 AM

Dear Venkatesh,

The minimum cross-sectional area of protective conductors (earth strip) shall be determined by the following formula:

S = (√I2t)/k

Where,

S = cross-sectional area, in square millimetres

I = value (a.c., r.m.s.) of fault current for a fault of negligible impedance, which can flow through the protective device, in amperes

t = operating time of the disconnecting device, in seconds

k = factor dependent on the material of the protective conductor, the insulation and other parts and the initial and the final temperatures.

k = 159 (for 200º C Max. Temperature) for Copper,

K = 105 (for 200º C Max. Temperature) for Aluminium,

k = 58 (for 200º C Max. Temperature) for Steel.

Note:

1) The initial temperature of the conductor is assumed to be 30 "C.

2) If application of the formula produces non-standard sizes, conductors of the nearest higher standard cross-sectional area shall be used.

3) Maximum permissible temperatures for joints should be taken info account.

Alternatively, value of k may also be calculated by:

k = √[Qc (B+20)/Q20) ln {1+(θf + θi)/(B+ θi)}]

Where,

Qc = Volumetric heat capacity of conductor material [J/ºC mm3]

B = reciprocal of temperature coefficient of resistivity at 0 ºC for the conductor ºC]

Q20 = electrical resistivity of conductor material at 20 ºC [Ωmm]

θi = initial temperature of conductor [ºC]

θf = final temperature of conductor [ºC]

Vinu_Answers Sure _Answers

__________________
Sure Answers Always
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: May 2011
Posts: 14
#3
In reply to #1

Re: Earth Strip calculation

06/10/2011 10:26 AM

Thank U , Very much sir . I am clear now

Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#4
In reply to #1

Re: Earth Strip calculation

06/13/2011 7:09 AM

Very good reply. It will be immensely helpful to Q4 Electrical Engineers.

Thanks,

Manindra

__________________
Manindra
Register to Reply
Active Contributor

Join Date: May 2011
Posts: 14
#5
In reply to #1

Re: Earth Strip calculation

06/15/2011 5:14 AM

The minimum cross-sectional area of protective conductors (earth strip) shall be determined by the following :

S = (It)/k

or

S = (I√t)/k

IN calculation the sqt and square will cancelled . so the above formula can also be mentioned . I hope i am right

Register to Reply
Commentator
Engineering Fields - Power Engineering - Power Engineering Passion Engineering Fields - Electrical Engineering - Engineering Passion India - Member - New Member

Join Date: Mar 2011
Location: Noida, (U.P.), India.
Posts: 99
Good Answers: 6
#6
In reply to #5

Re: Earth Strip calculation

06/17/2011 1:41 AM

Dear Venkatesh,

The minimum cross-sectional area of protective conductors (earth strip) shall be determined by the following formula:

S = {√(I2t)}/k

Hope, Formula is clear now.

Vinu_Answers Sure_Answers

__________________
Sure Answers Always
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Earth Strip calculation

06/10/2011 7:28 AM

British Standard 7671 is the only formula needed.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Apr 2012
Posts: 1
#7

Re: Earth Strip Calculation

04/25/2012 1:02 AM

Requested you explain this formula with some example.

Like: earth strip size for 500KVA Transformer/ for DG set & other small panels as per their load in KW.

Please clarify....

Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

manindra (1); PWSlack (1); sagirsiddique (1); venkatesh.a (2); Vinu_Answers (2)

Previous in Forum: Does Dielectric Strength Depend On Thickness?   Next in Forum: Performance of Motor With Soft Starter And Fluid Coupling

Advertisement