Power Cable or Signal Cable

06/10/2011 11:13 AM

hello, Is the connecting cable for smoke detectors connected in loops for fire alarm system consider as power cable or signal cable? thanks in advance.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: power cable or signal cable

06/10/2011 11:26 AM

Er, does it matter?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#2

Re: power cable or signal cable

06/10/2011 11:53 AM

Signal cable, usually run as power limited. Some of the older systems used power AND signal to the detectors. Most modern systems use a "signaling line circuit" whereby all detectors are on the same pair of wires, derive their operating power from them, and communicate their status using bi-directional bitstream data packets on them.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#3

Re: power cable or signal cable

06/10/2011 12:11 PM

Depends on the type of detector. Many units are 24VDC and power limited so the wire is considered signal cable. AC powered detectors may be 24V, 110V or 220V. Anything above 30V must be considered power cable.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#4
In reply to #3

Re: power cable or signal cable

06/10/2011 3:26 PM

That may have been true in the past. The only AC powered detectors sold today are for "single station" use, and several of them can be connected together with some models, or Duct Detectors, which can be powered by AC or DC. All spot type smoke detectors (Photoelectric and Ionization) sold today for connecting to a control panel are of the 24 VDC standard.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#5
In reply to #4

Re: power cable or signal cable

06/10/2011 4:13 PM

Are you talking about residential or commercial? I just installed 120VAC networked smoke detectors in my residence and bought them at Home Depot a month before. They utilize a third wire which is used to network the detectors, in lieu of a fire control panel.

At my facility, however, everything is run from 24VAC and run through control panels.

Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#6
In reply to #5

Re: power cable or signal cable

06/10/2011 4:37 PM

Yes, the residential detectors are 120 VAC, are considered "single station" devices, and can be interconnected with an additional wire. They almost always come with a 9 volt back-up battery. They actually operate on 9 volts DC all the time (even though it seems to the homeowner like they are running on 120VAC).

The commercial and industrial smoke detectors (as seen in every office building in the US) are all low voltage DC. If you have a fire control panel at your facility that feeds 24 volts AC to the detection circuits, you have a dinosaur and a system which will not meet any fire code in the USA. It is mandatory that all fire systems are battery backed. Batteries put out DC voltage, not AC. Your AC system will not have batteries. If it DOES have batteries, put a meter on the detector wires and you will find that they are DC.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#7
In reply to #6

Re: power cable or signal cable

06/10/2011 5:04 PM

Yes, very dinosaur, but that's how the government does things. That's why they don't write the code.

I double checked the drawings. I was thinking of our emergency power-off system, that's 24VAC for the shunt trips. The detectors are DC (and battery backed). Thanks for keeping me fresh on that.

It's always good to get into the drawings. (They're still paper, too...gov't style).

Register to Reply