Anonymous Poster #1

Main Reinforcement Direction

06/14/2011 5:26 AM

i know mostly direction of main reinforcement will be in shorter direction.but what direction it will be in case of isolated rectangular footing?(as there will be consideration of soil pressure)

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Aug 2009
Location: Glen Mills, PA.
Posts: 2385
Good Answers: 114
#1

Re: Main Reinforcement Direction

06/14/2011 10:45 AM

There will be a greater area in the long direction because the moment will be greater.

__________________
In a time of universal deceit, telling the truth is a revolutionary act. George Orwell
Reply
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#2

Re: Main Reinforcement Direction

06/14/2011 11:19 AM

Most likely the long direction. However, it depends on the relationship (geometry) between the footing and the column pier, transecting walls, or directly bearing column baseplate.

Each case must be assessed and analyzed on a case-to-case basis.

Don't forget that reinforcement is usually required in regards to both axis, as there are applied bending moments (and shear) present in each direction.

And don't forget to check and design for one-way shear, 2-way shear, and punching shear!

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Reply
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#3
In reply to #2

Re: Main Reinforcement Direction

06/14/2011 11:26 AM

I forget to include a very important factor in reinforcement of footings (and other concrete structural element)....

According to ACI 318 standard, minimum reinforcement ratio (Rho) for ASTM A615, Gr. 60 steel is 0.0033. Therefore, you'll need to reinforce the concrete element in both axis no matter what, unless you can demonstrate by analysis that the design tensile stresses doe not exceed the allowable tensile stress.

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.