gas fired gen

06/14/2011 9:32 AM

im planning to install a GE gas fired generator of 965 KW. i just wanted to know that whether the gas consumption vary with load applied. if so what will be the average difference (in %age )between gas consumption at 100 KW and 900 KW load?

Register to Reply
Pathfinder Tags: gas consumtion gas generator
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: gas fired gen

06/14/2011 9:35 AM

The fuel consumption will vary with load, though the variation may not necessarily be linear. Contact the manufacturer for the best advice.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: gas fired gen

06/14/2011 10:04 AM

I recommend that you contact General Electric (GE) with all of the pertinent information. We are not GE. We do not know anything about your specific generator nor do we have any responsibility or authority for this generator. We do not know if your gas fired generator will use gasoline, natural gas, propane, methane, hydrogen, acetylene, coal gas, or anything else that could be considered gas. I certainly do not care. I would expect that a 10% load will consume less fuel than a 90% load, but I would not expect there to be a linear relationship between the two fuel rates. There maybe a linear relationship with an offset but I would not count on my word for your budgeting calculations.

Actually I would not count on GE's word either. I would install sufficient instrumentation to measure the electric load and the fuel consumption rate. I would then measure your installation fuel consumption rates versus electric loads over time. I would likely set the initial installation results as the reference flow rates to set the bar for future comparisons.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#3

Re: gas fired gen

06/14/2011 11:44 AM

PWSlack and redfred have both given excellent advice. As redfred says, the manufacturer's information may not be all that accurate (they will provide the most optimistic information they can because they want you to purchase their product). A good source of information would be someone who already owns and operates a similar unit and has the operating data you seek.

The following approximations may be used for a VERY rough budgetary estimate The numbers are based on my experience with units from the 1960's-1980's; modern units with tighter emission controls may be different.

  • For a reciprocating piston-type engine, fuel consumption at idle (running with no load) is around 15% of full load. The consumption curve is a fairly linear increase of about 60% from idle up to around 90% load. Most engines are tuned for maximum efficiency at that point. The top 10% loading takes about 15% of the full load fuel rate.
  • For a combustion turbine, idle consumption is about 40%, and the curve is essentially linear from idle to full load.
__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Jun 2011
Posts: 69
#4

Re: gas fired gen

06/14/2011 3:26 PM

See Chart, it'll give you some sort of idea.

__________________
The early bird may get the worm, but the second mouse get's the cheese.
Register to Reply Score 1 for Good Answer
Participant

Join Date: Jun 2011
Posts: 2
#5

Re: gas fired gen

06/18/2011 9:09 PM

thank you every body. nice information.

ill try to contact GE. otherwise generator will run on natural gas.

Register to Reply
Register to Reply 5 comments

"Almost" Good Answers: