Two Transformer Operation with One NGR

06/17/2011 4:30 AM

Recently I got opportunity to visit Utility Substation with 02 nos of 40 MVA 132KV/33KV of which 01 is kept in service and other kept as reserve as total present load requirement is 30 MVA. This substation feeds to Industries which Import and Export power to grid.

The vector group of 40 MVA transformer is Yn/d1. The earth fault current of 33 KV system is limited to 700 amps by use of an earthing transformer with Zig-zag 33 KV primary connected to main transformer and neutral of earthing transformer is connected to NGR 27 ohm.

The installation has 01 NER which can be connected to any earthing transformers by switches between them.

If load on Utility increases (say 50 MVA) Is it possible to put both transformer in service feed from same Primary source and feeding two section of 33 KV Buses. In other words operation of 02 nos, 40 MVA transformer in service with respective earthing transformer and one common NER.

What could be problem in such arrangement.

It may be noted that transformer are not operating in parallel.

__________________
When was last time you did something for first time.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster #1
#1

Re: Two Transformer Operation with One NGR

06/17/2011 10:17 AM

It may be noted that transformer are not operating in parallel.

01 is kept in service and other kept as reserve

Do not these two statements contradict?

Register to Reply
Anonymous Poster #1
#2
In reply to #1

Re: Two Transformer Operation with One NGR

06/17/2011 10:23 AM

If they are in parallel then it is perfectly acceptable to use single NGR.

Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#3
In reply to #1

Re: Two Transformer Operation with One NGR

06/17/2011 10:29 AM

No. As stated in my question after load increase it is required to pot both in operation .

Primary of transformer shall be feed from same source where as secondary shall be feeding different section of 33 KV Switch gear.

__________________
When was last time you did something for first time.
Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#4

Re: Two Transformer Operation with One NGR

06/17/2011 10:30 AM

Out of curiosity, are there one or two zigzag transformers?

I'd rather see someone else answer your question--I think it can be done, but I've never seen it done. Maybe the rating of the NGR would have to be bigger (handle more power) than a similar NGR that could only ever see a ground fault from (to) one transformer.

Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#5
In reply to #4

Re: Two Transformer Operation with One NGR

06/17/2011 10:34 AM

You may have noted

"The installation has 01 NER which can be connected to any earthing transformers by switches between them"

So there are 02 Zig-zag earthing transformer.

__________________
When was last time you did something for first time.
Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#6
In reply to #5

Re: Two Transformer Operation with One NGR

06/17/2011 10:38 AM

Sorry, missed that!

Register to Reply Off Topic (Score 5)
Power-User

Join Date: Apr 2011
Location: Bengaluru, India
Posts: 128
Good Answers: 3
#7
In reply to #5

Re: Two Transformer Operation with One NGR

06/17/2011 11:17 PM

By ignoring the zig-zag impedance, the earth fault NER will be

= [33000/Sqrt(3)]/700 amps = 27.21 ohms.

Note the value of ohms depends purely on 33 kV and 700 ampers for limiting.

Thus you can use two transformers in parallel with a common NER, the current will still be limited to 700 ampers only , irrespective of number of transformer in parallel, as the voltage applied is still only a maximum of 33 kV/sqrt(3.0) under worst condition.

Further the impedance of the zig-zag transformer if any will further reduce the current below 700 A.

Trust this clarifies

__________________
Dr.Raghunatha Ramaswamy - We discover nothing new other than knowledge
Register to Reply Score 1 for Good Answer
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#8
In reply to #7

Re: Two Transformer Operation with One NGR

06/18/2011 1:59 AM

Dear Dr.Raghunatha Ramaswamy,

1. What would be value of fault current when two different phases of transformer (say R in Tr-1 and Y in Tr-2) develops Single phase to ground fault.

2. I have not worked on such arrangement with 2 TR and 1 NER. Have you?

__________________
When was last time you did something for first time.
Register to Reply
3
Power-User

Join Date: Apr 2011
Location: Bengaluru, India
Posts: 128
Good Answers: 3
#9
In reply to #8

Re: Two Transformer Operation with One NGR

06/18/2011 2:57 AM

I have not actually worked with two paralell transformers each with Zig-Zag transformer and with a common NER. I only know that on Delta Side, Zig-Zag provides a ground path and assume that the effect is similar to connecting the NER on star neutral side.

The calculations I have indicated are thumb rule calculations for Star Side Neutral Earthing Impedance calculations.

Your question

1. What would be value of fault current when two different phases of transformer (say R in Tr-1 and Y in Tr-2) develops Single phase to ground fault.

We can assume the zig-zag transformer as a star winding of a fictitious Star delta transformer , grounded through NER.

Your question implies that one of the transformer is having earth fault in R phase, and another in Y phase of second transformer. Both will provide a ground return path through the common NER.

The current through the NER will depend on the voltage at the star point to which it is connected. In the first case this voltage is vector sum of 2 voltages , i.e. Y+B , in the second case it is the vector sum of other two phases , i.e. R+B,

We can draw the sequence diagram of the arrangement and calculate or use a suitable computer program for the same.

It is very rare to consider simultaneous faults in fault calculations and protection design. So one need to work from fundamentals to obtain these results.

2. I have not worked on such arrangement with 2 TR and 1 NER. Have you?

Nor I have, but we can work from fundamentals.

__________________
Dr.Raghunatha Ramaswamy - We discover nothing new other than knowledge
Register to Reply Good Answer (Score 3)
Commentator

Join Date: May 2011
Posts: 84
Good Answers: 1
#14
In reply to #9

Re: Two Transformer Operation with One NGR

06/19/2011 11:04 PM

Dear Sir,

Considering he is using same NER for both the zig zag transformers. Then in case of earthfault on 33 KV system, total zero sequence thevenin impedance will contain

1. 3 times value of NER plus

2. equivalent impedance which is equal to parallel circuit of both zig zag trafo zero sequence impedance.

This total value will be less than the value which will be obtained considering only one zig zag trafo in line with NER.

Thus, fault current in case of earthfault will increase if both zig zag trafo are connected to same NER. But, It will be limited to 700 amps per NER rating.

Now i have a interesting ques here:

Now since fault current is increasing, fault MVA pf 33 kv bus is also increasing but since NER is limiting this fault current to 700 amps, then is it prudent to consider increased fault MVA ?

Will NER always limit the current to 700 Amps irrespective of whether it is L-G or LL-G fault?

Register to Reply
Power-User

Join Date: Apr 2011
Location: Bengaluru, India
Posts: 128
Good Answers: 3
#15
In reply to #14

Re: Two Transformer Operation with One NGR

06/19/2011 11:26 PM

The current is always determined by the voltage and impedance as per Ohm's law.

Consequently as long as the voltage remains same, NER value remains same, The current will remain same.

This has nothing todo with parallel arrangement or single circuit arrangment.

We are only interested in what is the voltage applied across the NER.

We may find out these by calculations.

Since there are 2 transformers in parallel, the positive seq , negative seq and zero sequence impedances of the transformers will become half. But the sizing of the NER has not considered any source impedance. Meaning, irrespective of the source impedance, the current will always remain under 700 Amps. The actual current will depend on source impedance also, which needs to be computed.

The 3 times NER value is in the zero - sequence network. Sizing calculations are done in phase domain assuming a single full phase voltage across the NER.

The increased fault MVA is only due to changes in the source impedance. But the fault MVA will still be restricted to a value limited by this 700 Amperes ceiling.

__________________
Dr.Raghunatha Ramaswamy - We discover nothing new other than knowledge
Register to Reply
Commentator

Join Date: May 2011
Posts: 84
Good Answers: 1
#16
In reply to #15

Re: Two Transformer Operation with One NGR

06/20/2011 3:17 AM

Then as per your saying,

Can he connect this 2nd trafo to 33 KV bus without any NGR connection through zig zag trafo..?

If this is the case suppose then, doesn't paralleling of these transformers on same 33 KV bus increases the fault MVA of this bus? Since +ve and -ve seq impedance are getting half. (considering identical transformers)

and i am also taking into account buscoupler of 33 KV bus as NC (normally close)

Register to Reply
Power-User

Join Date: Apr 2011
Location: Bengaluru, India
Posts: 128
Good Answers: 3
#17
In reply to #16

Re: Two Transformer Operation with One NGR

06/20/2011 4:06 AM

The fault level will increase due to parallel combination but still be less than 700 A. 700 A is the maximum fault level for single line to ground fault.

__________________
Dr.Raghunatha Ramaswamy - We discover nothing new other than knowledge
Register to Reply
Commentator

Join Date: May 2011
Posts: 84
Good Answers: 1
#18
In reply to #17

Re: Two Transformer Operation with One NGR

06/20/2011 4:58 AM

fault mva on respective bus is limited by ngr rating. I think that is why ner is rated as x amp for y sec. Now don't you think this ner is designed taking into account the fault current when only one transformer is operating? I am of view that ner is needed to be redesigned of different rating considering increased fault mva and fault current when two trafo are operating.

Register to Reply
Power-User

Join Date: Apr 2011
Location: Bengaluru, India
Posts: 128
Good Answers: 3
#19
In reply to #18

Re: Two Transformer Operation with One NGR

06/20/2011 5:06 AM

NO- NER is designed considering 0 source impedance or infinite fault MVA for the voltage considered. Hence it does not matter how may transformers are in parallel, the fault current will remain within the limit specified.

__________________
Dr.Raghunatha Ramaswamy - We discover nothing new other than knowledge
Register to Reply
Commentator

Join Date: May 2011
Posts: 84
Good Answers: 1
#20
In reply to #19

Re: Two Transformer Operation with One NGR

06/20/2011 6:52 AM

ok. now i got it. thanks for clearing my doubt. :)

Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#21
In reply to #16

Re: Two Transformer Operation with One NGR

06/20/2011 7:43 AM

Note also that the OP has stated that he is not planning to connect the transformers in parallel, they will feed separate (secondary) buses--from the OP:

If load on Utility increases (say 50 MVA) Is it possible to put both transformer in service feed from same Primary source and feeding two section of 33 KV Buses.

With respect to ground faults, I agree with raghunath7 that even paralleled, the ground faults will not increase.

However, if the transformers are paralleled to a common bus (perhaps by use of a NC tie breaker), the available fault current for non-ground faults will increase (the impedance of the transformer will be halved), so the ratings of the secondary bus and breakers would have to be re-considered.

Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#22
In reply to #21

Re: Two Transformer Operation with One NGR

06/20/2011 8:54 AM

Dear Mr rhkuma,

I have drawn the arrangement with 02 transformer secondaries, 02 Zig-zag transformers and 0ne NER for 02 cases,

1. When transformer operating in parallel i.e. Bus-coupler close.

2. When transformer operating independently i.e. Bus-coupler open.

Intrestingly, In both cases earth fault remain same but is case 1 the total fault current is divided among two Ziz-zag transformers and reach both main Transformers, whereas in case 2, the fault current flows only in circuit (section) under fault.

With such arrangement Earth fault current setting shall be a tricky job.

__________________
When was last time you did something for first time.
Register to Reply
Power-User

Join Date: Apr 2011
Location: Bengaluru, India
Posts: 128
Good Answers: 3
#23
In reply to #22

Re: Two Transformer Operation with One NGR

06/20/2011 9:28 AM

Assuming normal current through the NER under healthy condition is nearly 0.0, any current in NER that is reasonably beyond normal unbalanced condition can be considered as due to earth fault condition only.

The general practice is therefore, to set earth fault current setting at lowest/near lowest available current/plug setting and do the back up coordination using time dial setting. It is rarely a difficult situation.

__________________
Dr.Raghunatha Ramaswamy - We discover nothing new other than knowledge
Register to Reply Score 1 for Good Answer
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#10

Re: Two Transformer Operation with One NGR

06/18/2011 3:57 AM

Why don't you go for another NGR of identical parameters for ensuring dedicated NGR for each 40 MVA transformer so as to keep the scheme simple and reliable ?

This will also increase the operational flexibility, since failure of the single NGR will force you to switch OFF both the 40 MVA transformers.

__________________
Learning is a never-ending process.
Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#11
In reply to #10

Re: Two Transformer Operation with One NGR

06/18/2011 4:06 AM

Dear spradhan,

As mentioned in question, the facility belongs to Utility Co. So it is there choice to use one NGR.

It is always advantageous to have independent redundant system. In my opinion Saving one NGR and losing 100% redundancy s not a wise decision.

__________________
When was last time you did something for first time.
Register to Reply
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#12
In reply to #11

Re: Two Transformer Operation with One NGR

06/18/2011 4:38 AM

You are right.You may suggest this to the concerned Authority of the Utility Co. as a well wisher .

__________________
Learning is a never-ending process.
Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#13
In reply to #12

Re: Two Transformer Operation with One NGR

06/18/2011 4:40 AM
__________________
When was last time you did something for first time.
Register to Reply
Register to Reply 23 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: