LA rating

06/22/2011 2:10 AM

in 220kv switch yard why we are using 198kv LA?

like same for 400 kv why we are using 360 kv LA?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: LA rating

06/22/2011 2:14 AM

There must be a factor of 0.9 involved.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 11
#2
In reply to #1

Re: LA rating

06/22/2011 2:35 AM

yea that we know. why should use 0.9 factor?

Register to Reply
2
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3
In reply to #2

Re: LA rating

06/22/2011 9:58 AM

The LA Rating is selected on the formula:

Highest System Voltage (HSV) / Co-efficient of Earthing (Ground Fault Factor)

At EHV Levels, like 220kV & 400kV, the system will be solidly earthed and for solid earthing, the co-efficient of earthing is 0.8.

So, for 220kV Nominal System Voltage the HSV is 245kV. And, the LA rating will be: 245 x 0.8 = 196kV. The nearest standard LA available in the market is 198kV.

Similarly, for 400kV, the HSV is 420kV; and, the LA rating will be: 420 x 0.8 = 336kV; the nearest standard LA available in the market is 360kV.

Register to Reply Good Answer (Score 2)
Register to Reply 3 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); prabhurak (1); Tornado (1)

Previous in Forum: Pls Explian BDV TEST of transformer oil   Next in Forum: Disc insulator

Advertisement