transformer short circuit test

06/22/2011 2:24 AM

In short circuit test , what is the current will come in primary ,secondary. as secondary shorted. if 2500KVA,33KV/433V trafo %z 7.3 . what will be the current at secondary.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#1

Re: transformer short circuit test

06/22/2011 3:21 AM

The KVA of the given transformer under short circuit condition will be=2500/0.073

=34247 KVA

Therefore SC current on primary side=34247/(1.732X33) Amp

=599 Amp

Similarly,SC current on secondary side=34247/(1.732X0.433) Amp

=45665 Amp

__________________
Learning is a never-ending process.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2
In reply to #1

Re: transformer short circuit test

06/22/2011 3:46 AM

.......until the circuit protective device operates to disconnect it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Active Contributor

Join Date: Jun 2011
Posts: 10
#3
In reply to #1

Re: transformer short circuit test

06/22/2011 6:28 AM

thank you

Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 10
#4
In reply to #1

Re: transformer short circuit test

06/22/2011 6:30 AM

In short crt test secondary was shorted and currents to be measured in secondary side then how we will measure for this much amps through clamp meter?

Register to Reply
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#6
In reply to #4

Re: transformer short circuit test

06/22/2011 8:49 AM

Short ckt test is a Type Test and normally done in the Manufacturer's works or in recognised Testing Labs such as CPRI,ERDA,NEMA etc. I don't understand why you want to do it yourself and measure such high current through a clamp meter.Further, note that this will also reduce the life of your Transformer.

You may ask the Manufacturer to furnish a Type Test Certificate for similar design/rating Transformer alredy done by him for your reference.

__________________
Learning is a never-ending process.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#7
In reply to #4

Re: transformer short circuit test

06/22/2011 9:44 AM

Presuming that you are an electrical engineer, I am pretty sure that in your college days, this "Short Circuit Test" on a transformer is one of the very important Lab Excercises. Did you bunk the class, when this excercise was taught to you?

Register to Reply Score 1 for Good Answer
Associate

Join Date: Apr 2011
Location: Abu Dhabi, UAE
Posts: 25
Good Answers: 2
#5

Re: transformer short circuit test

06/22/2011 7:29 AM

Refer your text books once again and read how to perform short circuit test on your transformer. You should not apply rated primary voltage during this test.

For the transformer you have mentioned, if you apply 7.3 % of rated primary voltage to the primary winding, keeping the secondary shorted, you will find rated current flowing in both windings.

You can also search the web for transformer stability test.

Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); pravinba (1); PWSlack (1); spradhan (2); srinivas231 (2)

Previous in Forum: Disc insulator   Next in Forum: Insymmetrical Current

Advertisement