Busbar Sizing.

06/22/2011 4:35 AM

I really confused in busbar sizing.In our Previous company for aluminum busbar sizing we are taken 0.8A/Sq.mm, Cu Bus sizing-1.2A/Sq.mm. How the 0.8A/Sq.mm/Al. 1.2A/Sq.mm/Cu come.Is there any Standard or Calculation is Available.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Busbar Sizing.

06/22/2011 8:29 AM

Resistance of copper and aluminium!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Busbar Sizing.

06/22/2011 9:38 AM

Sizing busbars on such "thumb rules" such as 0.8A/sq.mm for Aluminium and 1.2A / sq.mm for Copper is very unprofessional and crude. There is a scinetific method of calculation on bus bar sizing depending on the continuous current rating - duly applying all rating factors, the short time withstand rating and the short circuit force withstand.

CR4 Admin: Removed Advertising

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#4

Re: Busbar Sizing.

08/01/2014 12:20 PM
Register to Reply