Transformer Synchronization

06/22/2011 2:06 PM

Dear Sirs,

I have 4.0 MVA, 33/11KVA Transformer at my site, now I would like to add one more same capacity transformer and keep both the transformers in synchronized condition. So in this situation, how to loading sharing will take place?

Should I add any special equipments in order to take place the load sharing in both transformers?

Kindly let me know, what are the parameters should be matched in both the txs.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Associate
India - Member - New Member

Join Date: Oct 2009
Location: INDIA
Posts: 49
Good Answers: 1
#1

Re: Transformer synchronization

06/22/2011 2:18 PM

As the transformer is power transferring devise there is no special conditions for connecting in parallel and the word synchronization is not correct. Provision of proper protection is necessary

__________________
key questions why, what & how - just think
Register to Reply
Participant

Join Date: Jun 2011
Posts: 2
#2
In reply to #1

Re: Transformer synchronization

06/22/2011 2:31 PM

Thanks for your reply. You correct that synchronization is not the correct word.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Transformer Synchronization

06/22/2011 3:06 PM

Here in lies a problem. For the protection of both transformers they are better off run separately but with the facility to inter connect them if needs be. Running the transformers permanently in parallel causes problems with the fault withstand of the existing panels.

The new transformer will need it's own switchboard so a way forward is to transfer half the load from Tx1 switchboard to Tx2 switchboard.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4

Re: Transformer Synchronization

06/22/2011 3:39 PM

If your goal is to have the transformers run in parallel it is important that they be as matched as possible. It is best if they are the same model number from the same manufacturer, at the very least they should have same rating and impedance to minimize the chance for less than perfect load sharing and the possibility of circulating currents due to minor manufacturing differences in the windings and core configurations/materials. Also keep in mind that as you parallel all these impedances that you don't create a dangerous situation where you expose everything to unanticipated high fault currents.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#5

Re: Transformer Synchronization

06/22/2011 3:51 PM

If the transformers have on-load tap changers (OLTC), then you should make sure they have controls installed to perform paralleling as well. If they don't the load tap changer controls and paralleling modules from Beckwith Electric are excellent. See their web site for info (I have no connection with Beckwith, but I have used their products with good results):

http://www.beckwithelectric.com/products/controls-ltc.html

As another reply stated, you also need to look at the combined fault current capability of the two transformers, and whether your bus, breakers, switchgear, etc., have adequate capability to withstand that. A 4MVA transformer at 11kV has only about 210amps full-load, so assuming 8%Z, it has available fault current of about 2625amps. Two transformers feeding into a fault would potentially double that, so your equipment may handle it. Now if you wanted to parallel two 40MVA transformers, that's another story...

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Commentator
Engineering Fields - Power Engineering - Power Engineering Passion Engineering Fields - Electrical Engineering - Engineering Passion India - Member - New Member

Join Date: Mar 2011
Location: Noida, (U.P.), India.
Posts: 99
Good Answers: 6
#6

Re: Transformer Synchronization

06/23/2011 2:08 AM

Parallel operation of transformers in three-phase system: Parallel operation means direct terminal-to-terminal connection between transformers in the same installations.

For successful parallel operation, three basic condition must be satisfied,

1) Transformers have the same phase-angle relation.

2) The same ratio with some tolerance and similar tapping range.

3) The same relative short-circuit impedance - percentage impedance - with some

tolerance.

(Reference: IEC-60076-8 Power transformers - Application guide)

It is to be noted that, If two transformers with slightly different ratios are energized in parallel, this will give rise to a circulating current between the transformers.

So, If you have planned to add one same capacity transformer, then there will be no issue.

If two or more transformer are connected in parallel, then load sharing % between them is according to their rating. If all are of same rating, they will share equal loads.

Vinu_Answers Sure_answers

__________________
Sure Answers Always
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#7

Re: Transformer Synchronization

06/27/2011 11:17 AM

In parallel operated transformers of same capacity, load sharing is rarely a problem, if their terminal volatges is taken care of. The problems in load sharing crop up in dynamic machines like generators. But, do please take care of their percentage impedances and vector group.

And, though alreday corrected, I would like to re-emphasise that for using the term 'synchronisation', at least one of the equipment should be a rotating electric machine. So, two transformers are never "synchronised" but only operated in parallel.

Register to Reply Score 1 for Good Answer
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); krishgunaa (1); parvathaneni (1); PeterT (1); RAMConsult (1); TonyS (1); Vinu_Answers (1)

Previous in Forum: Caterpillar Ecm Speed Governing   Next in Forum: Why We Run Motor in Delta Not in Star Connection
You might be interested in: Power Transformers, Transformers, Telecom Transformers

Advertisement