Transformer

06/24/2011 1:29 PM

Why the Transformer rating in KVA or MVA Not in KWH

Register to Reply
Pathfinder Tags: 3357
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Transformer

06/24/2011 1:40 PM

It can be, in one hour a 1000KVA or 1MVA transformer will give 1000KWHr at full load!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Associate

Join Date: Feb 2011
Location: Pune, Maharashtra, India
Posts: 32
Good Answers: 2
#2

Re: Transformer

06/24/2011 2:22 PM

Unlike motor which is defined based on active power requirement transformer is equipment which ment to transfer the power to loads I.e. Supply of both active and reactive power (losses). Hence, transformer, generators are rated in VA apparent power. You might be well aware of power triangle. Ref-BL Theraja-a text book of Electrical technology. Chapte-Transformers.

__________________
Engineering is an APPLICATION..
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#10
In reply to #2

Re: Transformer

06/27/2011 11:00 AM

Then what about Power Plant Generators, Mr. Salunkhe? Why are they rated in MW?

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: Transformer

06/24/2011 3:35 PM

If you discount the losses, the transformer without load would have a rating of zero.

What would that tell you?

Register to Reply
Associate

Join Date: Feb 2011
Location: Pune, Maharashtra, India
Posts: 32
Good Answers: 2
#4
In reply to #3

Re: Transformer

06/24/2011 6:42 PM

Is our transformer (equipments) made to run on no-load for it's life time? No. It's just a case of temp. Operation and transformer is always on-load. To clarify more, we do not select motor rating to run on no-load, but consider on -load rating with duty s1.

__________________
Engineering is an APPLICATION..
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#9
In reply to #3

Re: Transformer

06/27/2011 10:59 AM

You are misinterpreting, I fear! kVA is square root of the sum of kW square plus kVAR square. Even if you discount losses on a transformer without any load connected, it would still draw a very high reactive power (PF almost 0.5 lagging or lesser). Thus, it would still draw kVA and it is very correct to rate it in kVA.

Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 16
Good Answers: 1
#5

Re: Transformer

06/24/2011 11:42 PM

I believe that what you intend to ask is:

" Why transformers are rated in kVA or MVA, not in kW?" (kWH is kilowatt-hour...is a measure of power consumed in a certain length of time)

Power is computed as voltage(V) x current(I). 'Watt' will only be applicable to purely resistive loads. Considering almost all types of loads will have reactive component, thus, transformer power capacity will be rated in VA.

Register to Reply
Anonymous Poster #1
#6

Re: Transformer

06/25/2011 12:02 AM

1. This aspect has been covered, in great details in earlier CR4. I could give the link but then at least some effort must be put to search answer. There is atleast one thread on this and most likely several.

2. It looks like a class room doubt. Why don't you check back the text book?

3. Just think about what the transformer does. If you write the transfer equation of it you would find out the answer (BTW the same is true for any machine, motors, generators...).

It will show you what is transferred from input to output and what are the parameters affected (and what it does not affect at least in theoretical machine/equipment (in practical it may matter just a tiny bit)

Register to Reply
Commentator
Engineering Fields - Power Engineering - Power Engineering Passion Engineering Fields - Electrical Engineering - Engineering Passion India - Member - New Member

Join Date: Mar 2011
Location: Noida, (U.P.), India.
Posts: 99
Good Answers: 6
#7

Re: Transformer

06/25/2011 1:19 AM

kVA is the unit for apparent power. Apparent power consists of active and reactive power. Active power is the share of the apparent power which transmits energy from the source (generator) to the user. Reactive power is the share of the apparent power which represents a useless oscillation of energy from the source to the user and back again. It occurs when on account of some »inertia« in the system there is a phase shift between voltage and current. This means that the current does not change polarity synchronous with the voltage. But the heat generated in a winding as well as the eddy current losses generated in a transformer core depend on the current only, regardless of whether it aligns with the voltage or not. Therefore the heat is always proportional to the square of the current amplitude, irrespective of the phase angle (the shift between voltage and current). So a transformer has to be rated and selected by apparent power.

Vinu_Answers Sure_Answers

__________________
Sure Answers Always
Register to Reply Score 1 for Good Answer
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#8

Re: Transformer

06/25/2011 9:24 AM

"KW" has to be specfied alongwith power factor (PF).But a transformer can not have a fixed PF since it will depend upon the PF of various loads it feeds ,which will vary in the course of time depending upon the need as well as the type of loads.

However, rated MVA will remian same irrespective of the type of loads fed.

__________________
Learning is a never-ending process.
Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); electricalexpert65 (2); Salunkhem (2); spradhan (1); sulat (1); TonyS (1); Vinu_Answers (1); wareagle (1)