Low Voltage ACB Earthing

06/25/2011 3:26 AM

In case Low Voltage ACBs earthing terminals are provided on the case. In case of MCCBs no such arrangement is provided. So How do these devices function in case of earth fault

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Jun 2011
Posts: 10
#1

Re: Low voltage ACB earthing

06/25/2011 4:58 AM

Earthing terminal are provided on Cradle of ACB which is a made of Sheet steel & need earthing. On Breaker either ACB OR MCCB no earthing terminal is provided

Register to Reply
Commentator
Engineering Fields - Power Engineering - Power Engineering Passion Engineering Fields - Electrical Engineering - Engineering Passion India - Member - New Member

Join Date: Mar 2011
Location: Noida, (U.P.), India.
Posts: 99
Good Answers: 6
#2

Re: Low voltage ACB earthing

06/25/2011 4:59 AM

MCCB is "Moulded Case Circuit Breaker" and it is used for Power Switching applications.
It is available in a variety of continuous current ratings from 16A to 3200A and also with
short circuit breaking capacities ranging from 10kA to 75kA. They are capable of Making,
Carrying & Breaking Electric Currents in Circuits during Normal Conditions as well as during
abnormal or faulty conditions. An MCCB normally will have over current & short circuit
protection. Nowadays, MCCBs are also available with in-built earh fault protection.

A MCCB has a housing that is made from non conductive material. Available for low voltage
applications and comes in amperages from the single poles in the panel in your house to
3 phase and about 4000A.

__________________
Sure Answers Always
Register to Reply
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#3

Re: Low voltage ACB earthing

06/25/2011 9:00 AM

Earthing terminals are provided on the metallic body/enclosures/panels etc for safety of personnel by providing a path for any leakage current due to insulation failure in the concerned equipment.

These metallic parts are not supposed to carry any current under normal condition.Accordingly the metallic panels/enclosures housing ACB/MCCB/VCB are invariably provided with earthing terminals.But, earth terminals are never provided on the ACB/MCCB/VCB itself. You may note that in 4 pole ACB/MCCB Neutral terminal is also available in addition to the 3 phase terminals (But, no Earth terminal).

As regards functioning of the MCCB under earth fault condition, in-built current transformers will sense the fault & trip the MCCB if the earth fault protection release is provided therein.

Hope, this is clear.

__________________
Learning is a never-ending process.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: Low Voltage ACB Earthing

06/27/2011 10:54 AM

The other name for MCCB is totally insulated circuit breaker. In an ACB, the enclosure or case is metallic anbd hence during an earth fault, the fault curent might find a path thro the case, which might develop dangerous touch voltage hazards for human beings. To provide an alternate low impedance path for the fault current, one provides earthing connection to the ACB case.

Wheras in an MCCB as the case is made up of insulating material, no current can flow thro the case and hence no earthing terminal is required.

Register to Reply