HT Capacitors

06/25/2011 6:55 AM

Dear All,

One of the Steel Induction furnace plant, 22kv capacitors has all burnt.

Replacing new one, again, within one hour, 2 capacitors blasted!

Does any one gives the reason of failure ?

Electrical Data are :

System Volts - 22kV

Capacitors - 175 kvar - 7.5 KV * 2 nos. in series * 4 banks = 700kvar in each phase.

Connection of Capacitors - Star

Furnace KW - 5000 KW

Harmonics on LV side - Volts - 5% / Current - 10%

( As I learnt from manufacturer, capacitors can work up to 10% current harmonics.)

__________________
Exploring the Science of Electricity
Register to Reply
Pathfinder Tags: ht capacitors
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: HT Capacitors

06/25/2011 12:44 PM

Electrical furnace will produce a high level of harmonics. You need to have this checked before you smoke more capacitors. You will need someone experienced in this area to assist you. You will need to install tuned capacitor units depending on the harmonics generated. Why do you need the capacitors? Power factor Improvement?

http://www.google.com/search?sourceid=navclient&ie=UTF-8&rlz=1T4GZAZ_enUS396US396&q=electric+furnance+and+harmonics+and+capacitors

Register to Reply Good Answer (Score 2)
2
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#2

Re: HT Capacitors

06/26/2011 1:16 AM

Yep. Capacitors with not enough voltage safety margin well over and above the actual and nominal operating voltage can make a difficult day for you. Sit down with a sheet of paper, and try to add up the worst case INSTANTANEOUS voltages, line variation, harmonics etc. Add a hefty safety factor. THAT is the voltage rating you need.

On the other hand, all capacitors are ripple current limited. Lower internal resistances due more modern manufacturing IS NOT an advantage. That frequently allows in switching power supplies the allowed ripple current to be exceeded. It heats the cap, then it bursts. You can (shall?) measure the temperature rise. But do not be there bodily. Even a small one can go up, like a handgranade. After that you need to have a real heart-to-heart talk with the vendor's technician! I mean, both the furnace maker and the capacitor maker on the same line, at the same time, if you want resolution.

Good luck

Register to Reply Good Answer (Score 2)
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#3

Re: HT Capacitors

06/26/2011 1:55 AM

I know nothing about the harmonics involved, but you say "Capacitors - 175 kvar - 7.5 KV * 2 nos. in series * 4 banks = 700kvar in each phase."

As I interpret this, you have two 7.5 kV capacitors in series, and it sounds like you have four of these pairs connected in parallel for each phase. Two 7.5 kV capacitors connected in series can handle only 15kV with no safety factor, so of course they blow when connected to 22kV. Adding more capacitors or sets of capacitors in parallel does NOT make them withstand more voltage. You need four 7.5 kV capacitors in series to reliably withstand 22kv. Additional series sets of four can be used in parallel to obtain the capacitance needed.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 17
#7
In reply to #3

Re: HT Capacitors

06/27/2011 12:44 AM

I also presume as DK has said two 7.5 KV capacitors in series i.e. 22 KV

applied to them. How can they withstand 22KV.Further if only one capacitor

fails in a series system other capacitors are likely to fail immediately as 7.5 KV

is to to withstand 22 KV. Further the capacitive requirement cannot be fulfilled

as the capacitance is inversely proportional to the voltage.

As per above presumptions the capacitors will not withstand and need

redesigning. Further the question is for how long these capacitors being used?

Register to Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#8
In reply to #3

Re: HT Capacitors

06/27/2011 4:43 AM

Is this correct ?

Two capacitor with working voltage 7.5 kV , placed in series can withstand 15 kV. A 22 kV system voltage will normally destroy the capacitors.

BUT the capacitors are connected in STAR (wye) so the system voltage over the 2 series connected capacitors is only 22 / SQRT 3 = 12.7 kV ……

Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#9
In reply to #8

Re: HT Capacitors

06/27/2011 6:06 AM

Yes, and that would be 12,7kVeffective = 1,4 x 12,7 = 18,6kV peak. Thats why I asked the owner of the question in my reply, to sit down with pencil and paper, and add up all the INSTANTANEOUS voltages. Still waiting for his reply, while we try to guess!!!

Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#10
In reply to #8

Re: HT Capacitors

06/27/2011 9:54 AM

I missed that detail on my first reading of the post; the caps are indeed connected in wye. Of course you are correct.

I can't help wondering if there is any possibility that the replacements were wired in delta. Surely the replacement capacitors weren't rated 7.5 kV DC...

I can only imagine what it must be like to hear/see one of those blow...

Unfortunately, we have no idea whether the OP is seeing any of this!

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#4

Re: HT Capacitors

06/26/2011 8:47 AM

Yes, DK is right too. When you have a series/parallel arrangement of the capacitors, two added factors come into play.

Capacitors have tolerances. The plate on the cap has to say something like: 2 uF (micoFarad) +/-20%. If the lower parallel set happened to be at -20%, and the uppers at +20% by accident, the voltage is not divided evenly. Roughly speaking, the larger gets 20% less voltage, the smaller gets 20% overvoltage, and potentially blows. One gets around that by measuring each cap real capacitance, and mix and match before installation.

Capacitors, no matter how well made, have leakage current thru them, that allows extra voltage buildup over the better one. Not good. Standard solution for that is an extra parallel resistor carrying around 5 times of the highest expected leakage current, that usually occurs when everything is hot.

All of these leads back to the vendor's technical personnel. I would strongly hesitate to do any modification without them signing off on it. Much rather, let them do it, explain and demonstrate the necessary modifications and measurement.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jun 2011
Posts: 13
#5

Re: HT Capacitors

06/26/2011 10:43 AM

connect inductor in star pt. calculation of inductor depends on fault level of bus & gnd resistance value. generally manufacterer provide this data

Register to Reply
Guru

Join Date: Aug 2010
Location: Melbourne, Australia
Posts: 740
Good Answers: 24
#6

Re: HT Capacitors

06/26/2011 8:13 PM

The three factors which will destroy capacitors are:

1. Excess voltage

2. Excess ripple current.

3. heat from an external source

If the environment has not changed, and if your replacement caps are rated the same as the originals they should not blow unless there is another fault.

Measure the voltage and current on a good system, then the faulty on ..... trace it from there.

Register to Reply
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: