VFD

06/28/2011 7:05 AM

To run 180 KW VT pump motor i have two option, one is through VFD and other is through Soft starter.

So which is more better way to run the pump.

If i will select VFD then what are the other benifites of VFD over the Soft starter.

Please suggest the better way

Register to Reply
Pathfinder Tags: VFD versus Soft starter
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster #1
#1

Re: VFD

06/28/2011 7:23 AM

1. Energy efficiency- adds up every time you start and hence depends upon your number of starts

2. Better spped torque capacity at start - do-

3. The mechanical stress on components are much lesser due to more uniform speed pick up

4. variable speed (and hence variable flow rate)

5. possibility to have regenarative VFD too (but may not be much useful in pumping operation where the flywheel effect will be low)

Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#2

Re: VFD

06/28/2011 7:28 AM

VFD if you do not need to have pump run at full capacity all the time. If the work load the pump does varies with time.

Soft starter if it does run full capacity all the time as you have no need to vary the work the pump does.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: VFD

06/28/2011 9:55 AM

VFD will do the job of a soft starter in addition to its job of varying the frequency applied to the motor. A soft starter would do only soft starting. For apump application, there is tremendous scope for energy savings with a VFD, if your flow requirement is variable.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4
In reply to #3

Re: VFD

06/28/2011 12:33 PM

Post #3 is the best answer really. But the key is ONLY IF YOUR FLOW REQUIREMENT IS VARIABLE. If your flow requirement is constant, a VFD will WASTE energy for you. Also just to be clear, this ONLY applies to Centrifugal pumps, not to Positive Displacement pumps. Your statement indicating VT means it will apply to you, I only mention it for the benefit of others who may read this in the future.

Forget the anonymous comment on start-stop issues, there is NO energy savings issue associated with that, it's a common misconception. Both the soft starter and the VFD will soft start the motor which is good for everything, but will not make a difference in energy related cost. Soft starting saves on long term wear and tear on the mechanical components and is a good idea from that standpoint, and both technologies will accomplish that just fine.

the ONLY difference is as stated above; IF you have a variable flow situation. If you do, and you are using a valve to reduce flow, then reducing flow by slowing the motor with a VFD will reduce the losses associated with the valve and that will save you SIGNIFICANT energy. But of your flow is fixed and does not vary in your process, then there are no savings associated with a VFD and because the VFD consumes a small amount of energy due to internal losses (2-3%), the VFD will actually cost MORE to operate than a properly sized pump motor AND PROPERLY TRIMMED IMPELLER.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5
In reply to #4

Re: VFD

06/28/2011 8:22 PM

Thanks, Raef! But, OP's VT Pump could mean Vertical Turbine Pump and not necessarily Variable Torque. Isn't it?

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7
In reply to #5

Re: VFD

06/29/2011 4:55 PM

"But, OP's VT Pump could mean Vertical Turbine Pump and not necessarily Variable Torque. Isn't it?"

D'oh!

But then again, most Vertical Turbine pumps will be variable torque as well.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Anonymous Poster #1
#6

Re: VFD

06/29/2011 12:15 AM

There is a good article here which provides a good insight and comparison.

As far the efficiency issue, I will like to mention the principle of Variable Voltage variable Frequency operation (VFD) Vs Constant Frequency variable Voltage Operation (Soft Start)