Hoist Motor & Electrical Protection

06/28/2011 1:56 PM

AC Hoist motors are not contineously rated and have high, varying torque requirements. Are there specific considerations in providing Overload/Shortcircuit protections, and coordinating with upstream devices?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - USA! Hobbies - Musician - Sound Man Engineering Fields - Mechanical Engineering - More than a Hobby Technical Fields - Technical Writing - New Member

Join Date: Oct 2008
Location: City of Roses.
Posts: 2056
Good Answers: 101
#1

Re: Hoist Motor & Electrical Protection

06/28/2011 6:22 PM

Most of the protections are built into a quality hoist motor internally.

__________________
Don't believe everything you read on the Internet!
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Hoist Motor & Electrical Protection

06/28/2011 6:30 PM

If it has a nameplate, those are the minimum requirements.

If it doesn't have a name plate, don't use it.

What are "upstream devices"?

Register to Reply
Guru

Join Date: Dec 2007
Location: Mumbai, India
Posts: 1983
Good Answers: 25
#3

Re: Hoist Motor & Electrical Protection

06/29/2011 7:30 AM

You should provide bimetallic thermal relay for overload protection and HRC fuses for short circuit protection. O.L Relay can be of Siemens make and HRC fuses of English Electric make, both are reliable brands. More over you have to select the Hoist of suitable rating to suit your application. They are available as medium, heavy and steel mill duty ratings.

__________________
"Engineers should not look for jobs but should create jobs for others" by Dr.Radhakrishnan Ex President of India during my college graduation day
Register to Reply
Associate

Join Date: Jun 2011
Location: Canada
Posts: 38
Good Answers: 1
#4

Re: Hoist Motor & Electrical Protection

06/29/2011 9:30 AM

Hoist motors are compound wound or series wound for maximum torque from a dead start. This is why they draw huge power at startup and should have internal overload protectors for speed,power, and heat to achieve a government safety rating. The maximum current draw should be on the specification plate attached to the motor which is required by law. Shunt wound motors tend to be rated for continuous duty whereas series wound motors do not because of overheating and speed issues. Check out types of motors in an electrical engineering handbook or on internet.

__________________
Think Big, Dream Bigger, then Close the Gap
Register to Reply Score 1 for Off Topic
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7
In reply to #4

Re: Hoist Motor & Electrical Protection

06/29/2011 1:51 PM

He said in the beginning of his post that they are AC motors, not DC.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Associate

Join Date: Jun 2011
Location: Canada
Posts: 38
Good Answers: 1
#9
In reply to #7

Re: Hoist Motor & Electrical Protection

06/30/2011 9:21 AM

I am not an electrician most of crane information comes from "after the disaster" safety meetings. I am a tool and die maker who has to rely on the crane. Cranes and all other lifting devises have huge government safety regulations defining construction, installation, maintenance, certification, and use. Penalties for violating the regulations can be quite severe.

__________________
Think Big, Dream Bigger, then Close the Gap
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jun 2011
Posts: 13
#5

Re: Hoist Motor & Electrical Protection

06/29/2011 9:39 AM

Thanks

I agree that name plate takes care of standard protections required under manugacturers' and code guideline. Those guidelines normally address safety and equipmentprotection. Without being specific to a project, I was wondering whether there are additional considerqations for supply feeder to equipment such as hoist, elevator, etc. which are intermittent duty, but high frequent torque cycles. Supply feeder encompass switching equipment, cables and protective devices.

For example- which one is better - fuse, breaker or MCCB? Any starting considerations such as volt drop for enhanced life and performance of installation?

Register to Reply
Associate

Join Date: Jun 2011
Location: Canada
Posts: 38
Good Answers: 1
#6
In reply to #5

Re: Hoist Motor & Electrical Protection

06/29/2011 10:14 AM

All the applications you mentioned are industrial. I am not an electrician or electrical engineer. Where I have worked all the applications you mentioned always used industrial "Slow Blow Fuses" to handle the start up power surge. Most electricians do not like using circuit breakers for these applications because the breakers tend to stick with disastrous consequences.

__________________
Think Big, Dream Bigger, then Close the Gap
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jun 2011
Posts: 10
#8

Re: Hoist Motor & Electrical Protection

06/30/2011 12:29 AM

For Hoist motors duty calculations are as per AC4 duty. for selection of starters use TYPE2 coordination as well define the life of starter while selecting.

Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 13
#10
In reply to #8

Re: Hoist Motor & Electrical Protection

07/05/2011 11:17 AM

Any idea, how I get guide to AC4 duty calculation?

I assume it is European standard

Register to Reply
Guru

Join Date: Dec 2007
Location: Mumbai, India
Posts: 1983
Good Answers: 25
#11
In reply to #10

Re: Hoist Motor & Electrical Protection

07/06/2011 12:48 PM

Please refer to IS:3938 for Wire Rope Electric Hoist for various duty conditions.

__________________
"Engineers should not look for jobs but should create jobs for others" by Dr.Radhakrishnan Ex President of India during my college graduation day
Register to Reply
Register to Reply 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

JRaef (1); lyn (1); PSB (1); RVZ717 (1); suresh sharma (2); Trueheart (3); vorah (2)