Anonymous Poster #1

Selection of System Voltage for 50 Hz Country

06/28/2011 7:19 PM

Scenario:

A system is designed using pumps that run on a system voltage of 480 VAC, 60 hz (US). The motors are rated for 60 hz, eventhough most of the motors (but not all) and the most important ones are operated via VFD.

This system now goes to a country where the frequency is 50 hz and the voltage to run motors of the same capacity is 380 VAC.

You will get MV from the utility and so you are selecting the system voltage for the system to run the pumps.

The logic thing would be to take that MV down to the nominal 380 VAC 50 hz of that country as oppssed to bringnig it down to 480 VAC 50 hz.

Of course you will have to change the ratings of your motors to run on 380 VAC instead of 480 VAC.

The alternative, that is bringing the MV down to 480 VAC ending up with a system voltage of 480 VAC 50 hz, will give you a bizzare system voltage/rated frequency combination that no motor that i know of is rated for, namely 480 VAC, 50 hz.

What would you do?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United States - Member - USA! Hobbies - Musician - Sound Man Engineering Fields - Mechanical Engineering - More than a Hobby Technical Fields - Technical Writing - New Member

Join Date: Oct 2008
Location: City of Roses.
Posts: 2056
Good Answers: 101
#1

Re: Selection of System Voltage for 50 Hz Country

06/28/2011 7:52 PM

I would simply spec in motors with the correct Voltage and Frequency from the start.

__________________
Don't believe everything you read on the Internet!
Reply Good Answer (Score 2)
Associate

Join Date: Jun 2011
Posts: 48
Good Answers: 1
#2

Re: Selection of System Voltage for 50 Hz Country

06/28/2011 8:50 PM

first, i'm no electrical but as i understand motors will be used to drive pumps as mentioned here. before you proceed with your plan, consider this: you will have a problem on the the pump performance. changing the frequency means changing the speed. and speed is proportional to the pump capacity (reduced speed, reduced discharge flow) while your power consumption will be greatly decreased (this is good though) since power is proportional to the cube of the speed.

thanks and good luck!

Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#3

Re: Selection of System Voltage for 50 Hz Country

06/28/2011 10:00 PM

Unless you put a electronic converter, that takes care of frequency AND voltage increase, in the circuit, your 60Hz engine will not perform. Count max. 60%.

Besides this, when built for 60 Hz, it contains less iron and will run hot on 50 Hz.

__________________
Plenty of room here
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Selection of System Voltage for 50 Hz Country

06/29/2011 4:07 AM

Change the motors.

The performance of the pumps, i.e. their pressure/flowrate characteristic curve, will move downwards at the lower speed, and this may not be acceptable from the Process Engineer's perspective.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
5
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5

Re: Selection of System Voltage for 50 Hz Country

06/29/2011 2:47 PM

Motors work based on a V/Hz ratio. 460V 60Hz is essentially the same V/Hz ratio as 380V 50Hz, do the math. So 460V 60Hz motors will run just fine at 380V 50Hz, but they will run 20% slower. The power they consume will be less as well.

In a centrifugal (quadratic) pump, flow follows the cube of the speed change. So at 80% speed, the pump flow will become .8 x .8 x .8 = 51.2% of the flow that they would have at 60Hz. If you can live with that lower flow, no problem at all.

Having the VFD changes things a bit though. A VFD can produce any output frequency you like, so you could have 50Hz input and 60Hz output. But the problem is, it cannot change the maximum VOLTAGE. So if you input only 380VAC, the highest output you can produce will be 380VAC as well. That leaves you with a choice of either limiting the output frequency to 50Hz so that the it matches the motor V/Hz ratio, or changing the input voltage to be higher than 460V. The decision will depend on your need for flow. If all the pumps are doing is filling a tank, it may be acceptable to leave them running slower and taking longer to fill the tank. The net energy to do the work will be the same. But if the pumps need to overcome a specific amount of head pressure, and they needed full flow at the 60Hz design to accomplish this, then it won't work.

If you need full flow from the pump, you must change something. Changing the motors is foolish in my opinion because there are not a lot of places that use 380V 60Hz in the world, so replacement motors become rare and expensive. To me it would be far cheaper and easier to get some autotransformers on the front end of the VFDs to boost the voltage by 20% and set up the VFDs to put out 460V 60Hz. Chances are you will NEVER need to replace the transformers, then you have industry standard motors to work with.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 5)
Guru
United States - Member - USA! Hobbies - Musician - Sound Man Engineering Fields - Mechanical Engineering - More than a Hobby Technical Fields - Technical Writing - New Member

Join Date: Oct 2008
Location: City of Roses.
Posts: 2056
Good Answers: 101
#6
In reply to #5

Re: Selection of System Voltage for 50 Hz Country

06/29/2011 4:04 PM

I must say, that's worthy of a GA.

__________________
Don't believe everything you read on the Internet!
Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#7
In reply to #5

Re: Selection of System Voltage for 50 Hz Country

06/29/2011 10:45 PM

What will be the effect of replacing the impeller with a larger one?.

__________________
pnaban
Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#11
In reply to #7

Re: Selection of System Voltage for 50 Hz Country

06/30/2011 12:39 AM

if you want a increase the impeller you just as well get a bigger pump

__________________
The square root of nothing is what you make it!
Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#8
In reply to #5

Re: Selection of System Voltage for 50 Hz Country

06/29/2011 10:53 PM

Some versions (built in Europe) do have the voltage change upwards too. I use some here in the Bahamas. (Stephan electro - Think they come from Sweden)

__________________
Plenty of room here
Reply Off Topic (Score 5)
Power-User

Join Date: Oct 2010
Location: OZ, otherwise known as Oklahoma were the wind comes sweeping down the plains.
Posts: 159
Good Answers: 4
#13
In reply to #5

Re: Selection of System Voltage for 50 Hz Country

06/30/2011 12:51 AM

Flow is directly proportional to speed, Head (pump output pressure) changes at the square of the speed change, Horsepower required changes at the cube of the speed change. If you can live with the reduced performance of the pump then as JRaef says, operating the 60 Hz motors at 380 Volts 50Hz is fine. I agree that the rest of JRaef post is spot on, good answer.

Reply Score 1 for Good Answer
Associate

Join Date: Jun 2011
Posts: 48
Good Answers: 1
#14
In reply to #5

Re: Selection of System Voltage for 50 Hz Country

06/30/2011 1:13 AM

this might be an off-topic but i beg to disagree with your statement: "In a centrifugal (quadratic) pump, flow follows the cube of the speed change"

....in pumps or fan affinity laws for the same pump size, flow is just proportional with the speed, by formula:

Flow rate,Q1/Q2 = N1/N2,

which means when speed is reduced by 50%, flow rate is also reduced by 50%.

....it is the power consumption that is a function of the cube of the speed or:

Power, P1/P2 = (N1/N2)^3

Thanks!

Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2010
Location: Canada
Posts: 139
Good Answers: 6
#9

Re: Selection of System Voltage for 50 Hz Country

06/29/2011 11:16 PM

SO, what is the problem? ? ?
You have a VFD drive . . so set it to provide you with the required voltage and frequency.

That is what >Variable Frequency Drives< are for !!!

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#20
In reply to #9

Re: Selection of System Voltage for 50 Hz Country

06/30/2011 3:00 PM

"SO, what is the problem? ? ?
You have a VFD drive . . so set it to provide you with the required voltage and frequency.

That is what >Variable Frequency Drives< are for !!!"

Read my post above again.

You cannot feed a VFD with 380V and tell it to output 460V! It can change the Frequency to be anything up to 400Hz (mostly) but the voltage change can only be LOWER than the input, not higher.

If I could make one that could create voltage from thin air, I would be a rich man...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
2
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#10

Re: Selection of System Voltage for 50 Hz Country

06/30/2011 12:36 AM

The answer to your question is to use the Laws of Affinity as below...

Affinity Laws for a Speed Change

50 Hertz Capacity Flow = 50/60 X 60 Hertz Flow = 0.833 X 60 Hertz Flow

50 Hertz Head = (50/60)2 X 60 Hertz Head = 0.694 X 60 Hertz Head

50 Hertz HP Pump Load = (50/60)3 X 60 Hertz HP Load = 0.579 X 60 Hertz HP Pump Load

50 Hertz Motor HP Load = 50/60 X 60 Hertz HP Rating = 0.833 X 60 Hertz HP Rating

50 Hertz Motor Voltage = 50/60 X 60 Hertz Motor Volts = 0.833 X 60 Hertz Motor Volts

50 Hertz Motor Amps = Same as 60 Hertz Motor Amps

50 Hertz Pump Efficiency = Same as 60 Hertz Pump Efficiency

Note: These laws only apply to pump behavior - not to well or system performance.

you could also try this link

http://www.engineeringtoolbox.com/affinity-laws-d_408.html

FYI in the UK - 50Hz, 415volts, 3 phase.

Also I would suggest that you search CR4, these answers are there already, as this is a reply I gave last year to a similar question.

__________________
The square root of nothing is what you make it!
Reply Good Answer (Score 2)
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#12

Re: Selection of System Voltage for 50 Hz Country

06/30/2011 12:42 AM

Before you start thinking of using VSD/VFD's check the motor.. it may not be suitable for VFD/VSD operation and also check harmonic levels.

__________________
The square root of nothing is what you make it!
Reply
Power-User

Join Date: Oct 2010
Location: OZ, otherwise known as Oklahoma were the wind comes sweeping down the plains.
Posts: 159
Good Answers: 4
#15
In reply to #12

Re: Selection of System Voltage for 50 Hz Country

06/30/2011 1:55 PM

Most modern and quality 3 phase motors will handle VFD's, though there are VFD rated motors. Many VFD rated motors may only be standard motors that have been Horsepower de-rated. Do you mean electrical harmonics, or vibration harmonics? Vibration harmonics for a properly designed 60 Hz operated pump will be fine at 60 Hz, but have a problem at 50 Hz running speed. A properly designed VFD installation should not have electrical harmonic problems.

Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#17
In reply to #15

Re: Selection of System Voltage for 50 Hz Country

06/30/2011 2:19 PM

I mean electrical harmonics....

While what you write is all correct up until you say...A properly designed VFD installation should not have electrical harmonic problems.

I wish that was true... but unfortunately its not. VSD's do cause harmonics, and there are thousands of HMU's (Harmonic Mitigation Units) on the market all over the world, tuneable and fixed, to remove the harmful ones. The problem with harmonics it migrates to other power systems and costs money in lost power and damages other units/motors/electrical equipment on those power systems.

In an ideal world, and there are VSD's that have less than 5% TDH which is IEEE519 recommendations, out there, and they are becoming more prevalent in the market place as users are become smarter and greener.

In my industry, oil production using ESP's, we have motor and cable failures because of harmonics and bad power quality, some due to the generated HD caused by VSD's with no filters and numerous inductions motors at the end of VERY long lengths of cable (sometimes over 2 Kms).

Now by saying "properly designed" you mean it has filters or the drive has acceptable levels of harmonics then yes, but that means the user or purchaser has done his homework, or the supplier has sold the latest piece of kit that meets what will soon be an industry standard.

However not everyone is as clued up as we are, many people do not research alternatives or understand how things work. Thats why they ask questions on CR4

My words were cautionary ones, as these things have to be pointed out.

__________________
The square root of nothing is what you make it!
Reply
Power-User

Join Date: Oct 2010
Location: OZ, otherwise known as Oklahoma were the wind comes sweeping down the plains.
Posts: 159
Good Answers: 4
#19
In reply to #17

Re: Selection of System Voltage for 50 Hz Country

06/30/2011 2:56 PM

Of course I was speaking of VFDs with filters (reactors, isolation transformers) installed, and proper installation (cable size and length). Though a properly sized, quality motor will absorb most of the harmonics without problems.

Reply
Anonymous Poster #1
#16

Re: Selection of System Voltage for 50 Hz Country

06/30/2011 2:08 PM

The VFD driven motors of the system will run at the same speed whether the frequency is 60 or 50 Hz. Motors run under the rated speeds at 50 and 60 hz. That is not the issue. But it has more to do with the system voltage/frequecy you end up with.

Option 1: 480 VAC/50 hz

Option 2: 380 VAC/50 hz

I would go with option 2 in which case motors will have to be rated for 380 VAC; Option 1 is awckward combination, (agree?) The other reason is in case of motor replacement is needed you can more easily find 380 VAC, 50 hZ motors in that country that 480 VAC 50 hZ.

I ask, do you know of motors or transformers that are rated for 480 VAC 50 hZ? there will be other motors running without VFD (granted smaller motors ie 2, 3 hp) so again if your system is 480 VAC 50 hz i dont know that motors are rated for these ratings.

Any comments?

Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#18
In reply to #16

Re: Selection of System Voltage for 50 Hz Country

06/30/2011 2:23 PM

The VFD driven motors of the system will run at the same speed whether the frequency is 60 or 50 Hz.

Are you saying that the motor RPM is the same at 50Hz and at 60Hz???

__________________
The square root of nothing is what you make it!
Reply
Anonymous Poster #1
#22
In reply to #18

Re: Selection of System Voltage for 50 Hz Country

06/30/2011 3:58 PM

Again,

VFD driven motors will run at the same speed wheter 50 of 60 hz on the utility voltage by virtue of the VFD driving the motor at the set (desired) speed that our specific process requires. The speeds at which the motors are set to run for this process are below the rated motor speed wheter 50 or 60 hz, ie a 4 pole motor rated speed is about 1800 at 60 hz and 1500 rpm at 50 hz but we need that motor to run at 1400 rpm hence the VFD driving it. So whether the frequency if 50 or 60 Hz of the utlity the motor will run below its rated speed via the VFD.

i hope this clarifies.

Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#23
In reply to #22

Re: Selection of System Voltage for 50 Hz Country

06/30/2011 4:50 PM

I think the confusion comes from your statement..The VFD driven motors of the system will run at the same speed whether the frequency is 60 or 50 Hz.

If you had included the word..The VFD driven motors of the system will run at the same speed whether the SUPPLY frequency is 60 or 50 Hz.

then I would have understood it better.. let's put it down to a typo.. thank you for expanding... I two have dyslexic fungers!!

__________________
The square root of nothing is what you make it!
Reply
Power-User

Join Date: Oct 2010
Location: OZ, otherwise known as Oklahoma were the wind comes sweeping down the plains.
Posts: 159
Good Answers: 4
#21
In reply to #16

Re: Selection of System Voltage for 50 Hz Country

06/30/2011 3:08 PM

If we are talking 3 phase induction motors, then the motor speed is dependent on the number of electrical magnetic poles the motor has, 2, 4, 6, 8, etc and the power frequency. A 2 pole motor runs at approximately 3600 RPM on 60 Hz power, and approximately 3000 RPM on 50 Hz power. 4 pole - 1800 RPM at 60 Hz, 1500 RPM at 50 Hz, 6 pole - 1200 RPM at 60 Hz, 1000 at 50 Hz, etc.

Reply
Anonymous Poster #1
#24

Re: Selection of System Voltage for 50 Hz Country

07/05/2011 12:35 PM

My apologies...

Thank you for your understanding. Part of the reason why i am also siding with doing 380 VAC motors is becuase in my mind availability of 480 VAC (or 460 VAC i should say) motors, TX etc,s in that country maybe more difficult. BUT i need to do reasearch to see if this is a correct assumption.

NOW let's say that availability of 460 VAC rated equiptment is not a problem, say a 460 VAC rated motor-pump set , it problably will be rated for 60 Hz. it would not damage the motor to run at 50 Hz but it would run slower so...

Have any of you seen motors or TX rated for 460 VAC 50 Hz?

Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#25
In reply to #24

Re: Selection of System Voltage for 50 Hz Country

07/05/2011 1:59 PM

In the UK the supply voltage is 33Kv, 11Kv, 3.3Kv, 415V all 3 phase and 240v single phase all @50Hz.

To alter the voltage you require a transformer. But even USA manufacturers that make UK rated motors in the UK have a Nameplate voltage of 415v 3ph, so using a 480 volt motor 60Hz would require the application of the Affinity Law, or part of it, for power output, RPM and motor volts.

In answer to your last question... No, not a 50Hz.. 460v 60Hz, Yes

__________________
The square root of nothing is what you make it!
Reply
Power-User

Join Date: Oct 2010
Location: OZ, otherwise known as Oklahoma were the wind comes sweeping down the plains.
Posts: 159
Good Answers: 4
#26

Re: Selection of System Voltage for 50 Hz Country

07/05/2011 2:37 PM

Hey everybody, we seem to be forgetting that Anon's pumps in his system are are designed to run at 60 Hz. The system will not work as designed at 50 Hz. If Anon can live with the reduced performance of the system, then ok.

Reply
Anonymous Poster #1
#27
In reply to #26

Re: Selection of System Voltage for 50 Hz Country

07/05/2011 6:13 PM

i created some confusion. The pumps are in deed rated from the manufacturer to run 60 Hz. We are in the US so it is only natural to find motors rated at 60 Hz. We drive those pumps with VFD's at speeds lower than the rated speed at 60 Hz.

Reply
Guru
United States - Member - USA! Hobbies - Musician - Sound Man Engineering Fields - Mechanical Engineering - More than a Hobby Technical Fields - Technical Writing - New Member

Join Date: Oct 2008
Location: City of Roses.
Posts: 2056
Good Answers: 101
#28
In reply to #27

Re: Selection of System Voltage for 50 Hz Country

07/05/2011 6:37 PM

Pump's aren't specified by Hz, but by a given volume per revolution, max pressure and maximum RPM. If the pump is rated for 3600RPM, then I suppose you could say it's rated for 60Hz, but that's not really the common nomenclature.

If you calculate the lower RPM's for the 50Hz frequency drive, and get a reduced RPM, you'll then need to multiply that reduced RPM by the volume per revolution to get your reduced flow... If you can operate the equipment properly at this reduced flow, and the motors can run stable at the lower frequency, you should be ok.

And remember, pump's don't create pressure...

__________________
Don't believe everything you read on the Internet!
Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#29
In reply to #28

Re: Selection of System Voltage for 50 Hz Country

07/05/2011 6:42 PM

and that neatly brings us full circle to my post 10, the Laws of Affinity!

__________________
The square root of nothing is what you make it!
Reply
Anonymous Poster #1
#30
In reply to #28

Re: Selection of System Voltage for 50 Hz Country

07/05/2011 6:44 PM

Thank you. You are correct. Again i am not using my terms correctly. What i meant to say is that motors (not pumps) are rated for 60 Hz and/or 50 Hz.

and yes, pumps do not create pressure. Correctly if i am wrong again , pumps can overcome certain head pressure in front of them (as oppossed to creating it)

Reply
Guru
United States - Member - USA! Hobbies - Musician - Sound Man Engineering Fields - Mechanical Engineering - More than a Hobby Technical Fields - Technical Writing - New Member

Join Date: Oct 2008
Location: City of Roses.
Posts: 2056
Good Answers: 101
#32
In reply to #30

Re: Selection of System Voltage for 50 Hz Country

07/05/2011 7:57 PM

You are correct, Pumps only create flow, it's the downstream components that provide resistance to flow which create the pressure.

But you'll need both the correct pressure AND flow for your equipment to operate properly, and some pumps don't do well if they are being run at a lower speed than they were meant to run. A fixed displacement gear pump would be just fine running at a slower speed, but a fixed displacement vane pump requires a certain RPM to thrust the vanes out using centrifugal force in order to make the seal that will create flow, a vane pump cannot run at a reduced speed. Variable displacement pumps such as a piston pump with a swashplate are designed to operate at a constant speed, and would not do well (in most cases) being driven by a variable speed drive either. Many of your common trash pumps require a minimum RPM to operate correctly as well.

Your specific application may or may not work even if your motor's spin perfectly forever, all depending on the type of pumps you are running. I would hate to see you put a bunch of time and money converting the motors over to run 50hz, and find out the hard way that you needed that extra couple hundred RPM to operate your pumps the way you intended.

Just an FYI, I have no clue what your pumps are, and most likely you'll be just fine, but just in the off chance that Murphy has decided to leave my building and wander off to yours, you should be prepared for his arrival.

Murphy

-R

__________________
Don't believe everything you read on the Internet!
Reply
Power-User

Join Date: Oct 2010
Location: OZ, otherwise known as Oklahoma were the wind comes sweeping down the plains.
Posts: 159
Good Answers: 4
#31
In reply to #28

Re: Selection of System Voltage for 50 Hz Country

07/05/2011 7:35 PM

No, pumps aren't rated at a specific Hz, they are rated at a design condition at a specific RPM. Unless they are designed to operate using a VFD or other variable speed source, then they may be specified different design conditions, at different RPMs.

Reply
Reply to Forum Thread 32 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (5); brich (8); dvmdsc (2); Grand Poobah (6); JRaef (2); lito (2); olehwi (1); pnaban (1); PWSlack (1); RVZ717 (4)

Previous in Forum: Standard Medium Voltage Systems in Morocco and KSA   Next in Forum: Ultrasonic Sound
You might be interested in: DC Motors, Stepper Motors, AC Motors

Advertisement