Unbalanced 3 Phase Transformer Clarification

06/28/2011 8:11 PM

Please clarify the following for me:

If you have for some reason, an unbalanced 3 phase transformer, with different impedance windings and the neutral point is left floating, your neutral point will rise above earth potential and at some voltage X volts (depending on severity of imbalance)..

If the neutral point is grounded, your neutral point will be at earth potential, this what happens to this voltage which is the summation of the imbalanced phase voltages at the neutral point?

__________________
Electrical Engineer
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Unbalanced 3 Phase Transformer Clarification

06/29/2011 4:05 AM

If the neutral is grounded at the source, then the voltage at this place with respect to earth will be 0V. Any voltages w.r.t. earth elsewhere on the neutral are the result of currents flowing through the resistance of the neutral conductor, and simply an expression of unbalanced or mixed single-phase loads applied to the system.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#2

Re: Unbalanced 3 Phase Transformer Clarification

06/30/2011 11:11 AM

I can certainly understand unbalanced loads, but how do you get a 3 phase transformer with different impedance windings? Is this a home-made kluge made from three single-phase transformers, or perhaps a standard 3 phase transformer with one or more partially shorted windings? In either case, the transformer should be replaced!

The only other possibility I can think of would be where the three phases are not all connected to the same transformer tap number, perhaps trying to compensate for an unbalance on one phase.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Commentator

Join Date: May 2010
Location: UK
Posts: 89
Good Answers: 2
#3

Re: Unbalanced 3 Phase Transformer Clarification

06/30/2011 12:10 PM

What did you use to measure the transformer impedance? did you test/measure the voltage from its actual output, at the end of the cable attached to it, or did you calculate it?

Register to Reply
Commentator

Join Date: Jul 2010
Posts: 92
Good Answers: 1
#4

Re: Unbalanced 3 Phase Transformer Clarification

07/05/2011 9:34 PM

let me rephrase, if you have a transformer supplying various single phase loads between each phase and it's neutral point, and the number of loads between phase A and neutral is different to phase B and neutral, then you have unbalanced loads on the transformer.

My understanding is, with an ungrounded neutral point, there will be a voltage present on the neutral point of the transformer, as the vector sum of voltages for all 3 phases is no longer zero at the neutral point.

When you ground the neutral point, what happens to this voltage which results on the neutral point as a result of unbalanced loading on the transformer?

__________________
Electrical Engineer
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#5
In reply to #4

Re: Unbalanced 3 Phase Transformer Clarification

07/05/2011 9:56 PM

OK, now this sounds like a number of 120V single phase loads connected to the different phases of a 208V 3-phase transformer. If the neutral point is not grounded, then you can't guarantee 120V between any phase and neutral. The more heavily loaded phase will drop in voltage, and the other phases will rise. This could easily lead to destruction of some devices on the lightly loaded phase(s).

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Commentator

Join Date: Jul 2010
Posts: 92
Good Answers: 1
#6
In reply to #5

Re: Unbalanced 3 Phase Transformer Clarification

07/05/2011 10:41 PM

Yes I understand that, since the neutral point is floating, the voltage difference between phases and neutral is no longer the same. There is a voltage present on the neutral.

What happens to this voltage when the neutral is grounded? Does the voltage appearing at the neutral point, as a result of the unbalanced phases flow to ground?

__________________
Electrical Engineer
Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

dkwarner (2); polerz (2); PWSlack (1); thccontrols (1)

Previous in Forum: Ultrasonic Sound   Next in Forum: Variable Speed Pool Pumps

Advertisement