07/02/2011 6:07 AM
Sir, I have main electricity meter which have 15/5 and 250 kw. and three sub secure meter is attached having ct ratio is 150/5,200/5,100/5. reading take in kvah. but the matter is main electricity cumption is not equal to total consumption if sub meters. why?
Good Answers: 181
Re: meter reading
07/02/2011 7:31 AM
Re: meter reading
07/02/2011 8:22 AM
The metering errors are higher at lower loads so in order to match a sum of registrations of sub-meters wth a main meter it will be suitable to have load matching ct and also the kvah is a derived/calculated unit so its inherent error includes the error in active & reactive registrations.
Re: Meter Reading
07/02/2011 4:06 PM
Maybe a ground fault between the main meter and the others.