Isolation transformers

07/04/2011 1:17 AM

We are using Topaz MGE 1KVA isolation transformers. At the secondary side of the transformer, we observe 115V between Phase and Earth and 115V between Neutral and Earth. The Earth is kept isolated from both phase and neutral. Is this behaviour okay or there is something wrong?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Associate
Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Aug 2010
Location: INDIA
Posts: 38
Good Answers: 1
#1

Re: Isolation transformers

07/04/2011 1:35 AM

hello,

i think may be some problem is there in isolation transformer because voltage between phase and ground is not equal to the neutral and ground.

so, please check once before doing any further work on it.

in isolation transformer voltage on secondary side is same as primary side voltage because isolation transformer is having a turns-ratio of 1:1 with ferrite core.

__________________
knowledge is increased by sharing!!!!!!!!!!!
Register to Reply
Power-User

Join Date: Jun 2010
Location: Canada
Posts: 139
Good Answers: 6
#7
In reply to #1

Re: Isolation transformers

07/05/2011 8:39 AM

You must be off your rocker, . . . a power transformer using ferrite core!

That is a new one!

TOPAZ transformers are typically 120/120 or a 240/240 volt, . . . double shielded - to provide good isolation even at higher interference frequencies.

The degree of isolation you get - depends on your connections - proper connections!

Register to Reply
Commentator
Engineering Fields - Power Engineering - Power Engineering Passion Engineering Fields - Electrical Engineering - Engineering Passion India - Member - New Member

Join Date: Mar 2011
Location: Noida, (U.P.), India.
Posts: 99
Good Answers: 6
#2

Re: Isolation transformers

07/04/2011 4:11 AM

Obviously, there is something abnormal. You have mentioned that you have measured 115V between phase and earth and also between earth and neutral. but also you have mentioned that earth is kept isolated from both phase and neutral. Where is the third phase. Is this a single phase transformer. What is the current condition of the equipment.

Pl. give complete details of the conserned equipment and problem, when you raise any issue via post in any forum,

__________________
Sure Answers Always
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Isolation transformers

07/04/2011 4:29 AM

Many 3Ph star connected VT transformers up to 11KV only fuse red and blue phases on the secondary. Yellow being a link solidly earthed.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#4

Re: Isolation transformers

07/04/2011 7:21 AM

As many here have already mentioned, there just isn't enough information here to do a proper diagnosis. I don't know why people then jump on the idea that your transformer must have a fault. If these conditions are true then there may not be a problem with your transformer. But this is not the only combination of conditions that will give the symptoms you've described with a good isolation transformer.

  • The primary voltage being applied to your single phase transformer is 230VAC RMS.
  • The instrument you are using to measure this voltage has a very high input impedance.
  • The secondary windings has a lower insulation resistance to ground than the input impedance of the meter.
  • Somewhere downstream of your transformer there is a device with a balanced lower impedance to ground than your test instrument.
__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Active Contributor

Join Date: Jun 2007
Posts: 24
#8
In reply to #4

Re: Isolation transformers

07/05/2011 9:25 AM

I think the first two conditions given by you are TRUE. I have connected 230V ac supply to primary. I am using a Fluke multi-meter with very high input impedance. (I have to check the specs to give you the exact value). the other two conditions also may be true because of the high impedance of the fluke multi-meter.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5

Re: Isolation transformers

07/04/2011 12:01 PM

How about this? It's a 3 phase 208V Wye (star) secondary, the Neutral is grounded, but at a different location than the EGC (as it should be). But there is a ground potential difference that just happens to make the Neutral to Ground reading 115V. For example it has a Neutral Grounding Resistor.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
3
Power-User

Join Date: Oct 2007
Posts: 102
Good Answers: 8
#6

Re: Isolation transformers

07/04/2011 11:17 PM

Thanks for the xfmr model. Google data shows 60dB interferance attenuation.

It seems reasonable that L&C filters as well as electrostatic screens will be in the enclosure.

How about checking the capacity to earth (unenergised) of the output terminals?

Expect ca. 10nF.

That would give half secondary voltage on a 10M ohm multimeter, so I guess it is a 230V connected secondary.

If you prefer, try shorting the neutral terminal to earth (transformer energised). You would expect no problen with an isolation transformer.

Disconnect the short and measure the current to earth from neutral. With the 115V, current and mains frequency calculate the capacity.

To have full benefit from the noise attenuation spec. maybe twin screened cable to the load should be used.

How about a quick word to the person who specified such a special device?

You would probably be guided well.

Register to Reply Good Answer (Score 3)
Active Contributor

Join Date: Jun 2011
Posts: 13
#9

Re: Isolation transformers

07/05/2011 10:40 AM

isolation xformer ph & neutral are grounded with ir value, so it gives voltage as you are measured. draw ground connection with ir value with your ph & neutal of isolation xformer & study drawing. then you will understand why you are getting voltages.

Register to Reply
Register to Reply 9 comments