Urgent Help ! - Grounding of 2 Engine Starting Batteries Connected In Series

07/04/2011 2:06 AM

Dear All,

I have currently 2 Engine starting batteries connected in series.

Do i need to ground my batteries?

How do i connect the batteries to ground?

Should i connect the negative terminal of the battery to ground?

Kinda confused with how grounding works for batteries.

Hope to hear from you guys soon as i am testing my genset very soon !

Thanks !

Alan

__________________
There is no limit towards how much one can learn.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#1

Re: Urgent Help ! - Grounding of 2 Engine Starting Batteries Connected In Series

07/04/2011 2:59 AM

If they are in series than only one terminal would be grounded.
E.G if its a negative earth the connections would go:-

Ground connected to negative of battery1.
Positive of battery1 joined to negative of battery2
Positive of battery2 which then connects to you load (starter motor?) postive terminal (via switch).
Load negative trminal will be connected to ground completeing the circuit.
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Associate

Join Date: Jun 2009
Location: Singapore
Posts: 36
#3
In reply to #1

Re: Urgent Help ! - Grounding of 2 Engine Starting Batteries Connected In Series

07/04/2011 4:29 AM

Hi Guys,

I just did the grounding of the battery cables and sadly there is a short circuit.

I have connected the positive terminal of battery 1 to the motor then the negative terminal of battery 1 to positive terminal of battery 2 and then the negative terminal of battery 2 to the battery disconnect switch.

After which , i connected the negative terminal of battery 2 to ground. But this causes a massive short circuit.

Could it be because my load is not grounded?

Therefore, the current is short circuited to ground?

__________________
There is no limit towards how much one can learn.
Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#4
In reply to #3

Re: Urgent Help ! - Grounding of 2 Engine Starting Batteries Connected In Series

07/04/2011 4:39 AM

What is the application? Could it be that you have an old system using a positive ground, and there's still another ground connection in the system?

Also, check where the other (non-battery) side of the disconnect switch is wired to.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #3

Re: Urgent Help ! - Grounding of 2 Engine Starting Batteries Connected In Series

07/04/2011 6:48 AM

Meter ohms between the wire that has been disconnected from the battery positive terminal and ground. Remove all downstream connections between this wire and ground before re-energising the circuit.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #3

Re: Urgent Help ! - Grounding of 2 Engine Starting Batteries Connected In Series

07/04/2011 9:39 AM

For a positive-ground circuit, meter the negative wire instead. See Fredski's sketch below.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#12
In reply to #3

Re: Urgent Help ! - Grounding of 2 Engine Starting Batteries Connected In Series

07/04/2011 1:04 PM

From your description it appears that you connected starting relay at the negative battery pole. Although you may have already fried alternators, please stop now before you fry everything and seek professional electrician help, because I don't think you understand basics. If you don't stop now, other professional help type is on it's way. S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#24
In reply to #1

Re: Urgent Help ! - Grounding of 2 Engine Starting Batteries Connected In Series

07/05/2011 2:01 PM

That statement only holds true for a negative grounding system. Putting the positive end to the chassis as its common ground will be true for a positively grounded system.

It is very common to encounter a positively grounded system in the olden days, where the positive terminal of the battery were tied down to the chassis of the vehicles and used as the common ground.

__________________
vsar
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#2

Re: Urgent Help ! - Grounding of 2 Engine Starting Batteries Connected In Series

07/04/2011 3:46 AM

Just to clarify what Del said (which is perfectly correct) - the "ground" here need not be (and usually isn't) the same as the electrical safety ground used in mains power systems. It would typically just be the vehicle chassis.

Also, there is often a (high current-carrying capacity) wire connecting the load negative to the battery negative, rather than relying only on the connection through the chassis. This is in addition to the ground connection.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Associate

Join Date: Aug 2010
Location: bhubaneswar
Posts: 34
Good Answers: 1
#5

Re: Urgent Help ! - Grounding of 2 Engine Starting Batteries Connected In Series

07/04/2011 6:47 AM

Hi, I think what the DEL said is right.you can do like that and another things you should have sure that starting motor is ok.just take the multimeter and check the short circuit of motor and go proceed acoording to del for connecting the batteries in series.no need to ground the batteries just connect the batteries in series to get the required dc voltage.

thanking you.

Register to Reply
2
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#7

Re: Urgent Help ! - Grounding of 2 Engine Starting Batteries Connected In Series

07/04/2011 7:02 AM

something like this.

Register to Reply Good Answer (Score 2)
Associate

Join Date: Jun 2009
Location: Singapore
Posts: 36
#9
In reply to #7

Re: Urgent Help ! - Grounding of 2 Engine Starting Batteries Connected In Series

07/04/2011 11:23 AM

Hi.

This is exactly what i did.

But there was a short circuit at the negative terminal when i connected this way.

what could be the reason that cause this?

__________________
There is no limit towards how much one can learn.
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#10
In reply to #9

Re: Urgent Help ! - Grounding of 2 Engine Starting Batteries Connected In Series

07/04/2011 11:31 AM

Lets make sure we're talking about the same thing. What EXACTLY do you mean by "short circuit"? If any load is in the circuit, like a door lamp, radio, etc. you'll see a spark when you complete the circuit.

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#11
In reply to #10

Re: Urgent Help ! - Grounding of 2 Engine Starting Batteries Connected In Series

07/04/2011 11:36 AM

Agreed - and this is even more apparent if the load is a starter motor!

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Associate

Join Date: Jun 2009
Location: Singapore
Posts: 36
#13
In reply to #10

Re: Urgent Help ! - Grounding of 2 Engine Starting Batteries Connected In Series

07/04/2011 8:12 PM

When i completed the circuit, there is a spark at the negative terminal of the battery where the grounding cable is connected to...

__________________
There is no limit towards how much one can learn.
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#14
In reply to #13

Re: Urgent Help ! - Grounding of 2 Engine Starting Batteries Connected In Series

07/04/2011 8:20 PM

Tell me what the LAST thing you connected to complete the circuit was. And where EXACTLY did you see the spark? I wish I had a picture of this. If the "spark" came from anywhere besides the last connection being made you have a bad connection at that spark. Possibly a faulty/grounded part.

Register to Reply
Associate

Join Date: Jun 2009
Location: Singapore
Posts: 36
#15
In reply to #14

Re: Urgent Help ! - Grounding of 2 Engine Starting Batteries Connected In Series

07/04/2011 10:08 PM

Ok.

The last thing i did was to connect the grounding cable from ground to negative terminal and there was spark at the negative terminal of the battery.

Anyway , I had did a check with my multimeter and i realised that my system is positively-earthed.

Is that normal?

__________________
There is no limit towards how much one can learn.
Register to Reply
Guru
Engineering Fields - Nuclear Engineering - New Member

Join Date: Sep 2009
Location: Louisville, OH
Posts: 1925
Good Answers: 36
#17
In reply to #15

Re: Urgent Help ! - Grounding of 2 Engine Starting Batteries Connected In Series

07/04/2011 11:38 PM

A positive ground is not abnormal on older vehicles. How old is the one you are working on? I collect antique fire apparatus, and some are positive ground (and some are negative ground.) Most newer vehicles are negative ground from the factory, but not the old stuff.

Check that disconnect too. It is normally put in the hot wire, but could be put in the ground wire. If someone added the disconnect to a positive ground vehicle, he may have put it in the "wrong" place, and thus confused you!

Trace all wires if you haven't already.

__________________
Lehman57
Register to Reply
Associate

Join Date: Jun 2009
Location: Singapore
Posts: 36
#18
In reply to #17

Re: Urgent Help ! - Grounding of 2 Engine Starting Batteries Connected In Series

07/05/2011 12:58 AM

Erm.

I am using the batteries on a Caterpillar genset which is manufactured in 2010.

I would define the spark as a big spark.

The cable lug instantly burnt off upon contact and the battery terminal melted too...

__________________
There is no limit towards how much one can learn.
Register to Reply
Guru

Join Date: Feb 2011
Location: Atlanta, GA
Posts: 1053
Good Answers: 110
#26
In reply to #18

Re: Urgent Help ! - Grounding of 2 Engine Starting Batteries Connected In Series

07/05/2011 4:36 PM

STOP.

__________________
Think big. Drive small.
Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#22
In reply to #15

Re: Urgent Help ! - Grounding of 2 Engine Starting Batteries Connected In Series

07/05/2011 8:53 AM

There is your answer; "Anyway , I had did a check with my multimeter and i realised that my system is positively-earthed."

Your system is polarized with a positive grounded system. Although the batteries are properly connected in a series manner, the final two + and - resulting terminals should be connected as follows;

The positive end of your battery should be the one connected to the ground and the Negative end direct to the load (starter motor).

To avoid any further damage, make sure to check and verify that the positive terminals of any other electrical loads are also grounded like your starter motor - meaning you have a "positive ground" electrical system in place.

__________________
vsar
Register to Reply
Guru
Engineering Fields - Nuclear Engineering - New Member

Join Date: Sep 2009
Location: Louisville, OH
Posts: 1925
Good Answers: 36
#16
In reply to #13

Re: Urgent Help ! - Grounding of 2 Engine Starting Batteries Connected In Series

07/04/2011 11:28 PM

Just how big is this "spark?" A little thing can be a light bulb, or maybe the vehicle computer if it's new enough. A big spark that makes you jump into next week may be a short or maybe the starter if the start button/switch/relay is stuck.

The advice to get a competent electrician is good.

__________________
Lehman57
Register to Reply
Commentator

Join Date: May 2008
Location: South Silicon Valley
Posts: 87
Good Answers: 3
#20
In reply to #16

Re: Urgent Help ! - Grounding of 2 Engine Starting Batteries Connected In Series

07/05/2011 2:44 AM

Sure sounds like you are connecting the final connection point while a large load is engaged. As suggested above, look to see that you have a switch/starter button or such that will make the final connection, not the ground cable being the final connection.

Register to Reply
Power-User

Join Date: Jan 2010
Location: Atchison Village
Posts: 383
Good Answers: 39
#19

Re: Urgent Help ! - Grounding of 2 Engine Starting Batteries Connected In Series

07/05/2011 1:07 AM

If you need 24 volts to start the engine, you're in over your head right now. STOP! You're looking at possible injury from exploding acid batteries, fire, and massive expense for fried equipment in milliseconds!

__________________
Align culture with nature...
Register to Reply
Guru

Join Date: Aug 2007
Location: London England.
Posts: 583
Good Answers: 10
#21

Re: Urgent Help ! - Grounding of 2 Engine Starting Batteries Connected In Series

07/05/2011 3:19 AM

When you are grounding batteries the negative goes to the engine block & the live to the solenoid on the starter, when you operate the solenoid the circuit is made,but make sure you connect the batteries correctly:- Neg to block, Pos to Neg of second battery, Pos to solenoid or switching panel which ever way it's wired.

__________________
When I die I'd like to go peacefully in my sleep like my dad,not shouting and screaming like his passengers.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#23

Re: Urgent Help ! - Grounding of 2 Engine Starting Batteries Connected In Series

07/05/2011 12:52 PM

You are unqualified to work on this problem (already mentioned by someone). It could get extremely dangerous for you. Go and get a professional before you regret it for the rest of your life.....

Batteries of these types are a huge source of energy when shorted out!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2011
Location: Atlanta, GA
Posts: 1053
Good Answers: 110
#25

Re: Urgent Help ! - Grounding of 2 Engine Starting Batteries Connected In Series

07/05/2011 4:34 PM

I will echo the sentiments of others. Don't do this work yourself. You should not be working on a Caterpillar genset, all of which produce lethal voltages and can create arc blast hazards as well.

A qualified individual will be certain how to hook up a battery, will be certain about the the machine's having negative or positive ground, and will not encounter large sparks when hooking things up. A qualified individual will ordinarily ensure that there is no sparking near the battery upon hookup, by making the final connection away from the battery (such as at the machine end of the grounding cable, rather than at the battery end. ) A qualified individual would be able to supply a schematic of what he is attempting to do.

You are lucky that the batteries did not explode.

__________________
Think big. Drive small.
Register to Reply Score 1 for Good Answer
Register to Reply 26 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (1); Bazzer Englander (1); Fredski (3); JohnDG (3); K_Fry (2); Lehman57 (2); liukawa (5); manvendra (1); Not too Smart (1); ormondotvos (1); PWSlack (2); SimpleMind (1); user-deleted-1105 (1); vsar (2)