BDV of Transformer Oil at 4mm Gap

07/05/2011 8:38 AM

how much BDV of transformer oil at 4mm gap.

why we use 2mm or 4mm gap between electrodes ?

Register to Reply
Pathfinder Tags: bdv value of oil at 4mm gap
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: BDV of Transformer Oil at 4mm Gap

07/05/2011 9:29 AM

Vide IS 6792:1992, the minimum BDV of transformer oil across a contcat ghap of 2.5mm shall be:

30kV for voltages uptp 72.5kV

40kV for voltages above 72.5kV upto 170kV

50kV for voltages above 170kV upto 420kV

Register to Reply
Commentator
Engineering Fields - Power Engineering - Power Engineering Passion Engineering Fields - Electrical Engineering - Engineering Passion India - Member - New Member

Join Date: Mar 2011
Location: Noida, (U.P.), India.
Posts: 99
Good Answers: 6
#2

Re: BDV of Transformer Oil at 4mm Gap

07/06/2011 3:51 AM

Bureau Of Indian standards, has set some norms for determining any process or activity that has to be accepted by all the industries manufacturing, supplying any product on commercial level.

For your question, IS-6792 describes the method of determining the electric strength of insulating oils. It clearly states that, the gap between the two electrodes (copper, brass, bronze or stainless steel polished) must be set within 2.5±0.01mm.

So, It is clearly mentioned in the standard to take BDV at 2.5±0.01mm, then why you want to conduct it at 4mm?

Now, Suppose if were a oil manufacturer and you conduct BDV testing at 4mm which not conforms to Indian or any globally accepted standards, then why customers will purchase your oil?

Vinu_Answers Sure_Answers