MCCB Rating Selection - Incomer - Outgoing Coordination

07/06/2011 3:47 AM

I have to select one MCC/panel incomer and outgoing with MCCB. Is there any regulation applicable regarding selection and cordination of incomer MCCB and outgoing MCCB rating ? Is there any IEC /BIS code defining the minimum MCCB outgoing feeder rating in comparison to Incomer MCCB rating - i mean ratio of outgoing MCCB rating to Incomer MCCB rating ? Can I have 630 A MCCB as incomer and 25 A MCCB outgoing?

If any body can help with refernce to relevant IEC guidelines, it would be appreciated .

Thanks,

Krishna varma

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: MCCB rating selection- Incomer -outgoing cordination

07/06/2011 5:13 AM

As far as i know, IEC does not specify nor recommend any discrimination guidelines. If you think about it, it is a user's choice, since a very good discrimination system will be more expensive than a somewhat simpler cascading one. All design is a trade-off between conflicting requirements.

A very good paper on discrimination is here:ECT 167

As far as i know, Schneider guarantees discrimination between upstream and downstream breakers which are rated 2.5:1. LSIS claims 1.6:1.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: MCCB Rating Selection - Incomer - Outgoing Coordination

07/06/2011 9:44 AM

Why should there be any regulation for sizing the Incomer MCCBs and/or the Outgoing MCCBs in a particular ratio?

Imagine you have a 2500kVA, 11kV/433V Transformer feeding a PCC (Power Control Centre) and from this PCC you also have to feed a small lighting panel, say, of 100A. The incomer ACB should be of 4000A rated current and with a short circuit breaking capacity of about 60kA (Assuming 6% Impedance of the transformer). And, the outgoing feeder in this PCC for the above lighting panel should have a continuous rated current of 100A and with a breaking capacity of 60kA.

The problem with MCCBs would be that a 100A MCCB Frame Size may not have a beaking capacity of 60kA; so, you may have to go for a higher frame size MCCB of, say, 400A, with a breaking capacity of 60kA and set the over current release of this 400A MCCB to 100A to have effective over current protection. This is how it is solved.

But, if the outgoing feeder is a Switch-Fuse-Unit, you don't have any problem as even a 100A HRC fuse would have a breaking capacity of 80kA or more.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#3

Re: MCCB Rating Selection - Incomer - Outgoing Coordination

07/06/2011 11:23 PM

As a rule of thumb the incoming > 1.6 times the outgoing but you can use MCCB with adjustable settings & suitable KA rating.

__________________
pnaban
Register to Reply
Commentator

Join Date: Jun 2011
Posts: 67
Good Answers: 2
#4

Re: MCCB Rating Selection - Incomer - Outgoing Coordination

07/07/2011 12:25 AM

Following steps can be taken-

1) Calculate fault level at the incomer of the MCC.

2) You can assume the same fault level at the outgoing.

3) Plot this fault current on the trip characteristic of the outgoing breaker.

4) Check the total load current on the MCC and the largest starting current of the motors starting together.

5) The incomer trip characteristic should not trip under 4) above and should also be clear of the fault current trip curve of any of the out goings. This is called discrimination between incomer and outgoing breaker. Select an incomer size which fulfills these conditions.

6) My experience suggsts that the incomer can be twice the size of the outging provided it is more than the full load current of all ougoings.

Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 13
#5

Re: MCCB Rating Selection - Incomer - Outgoing Coordination

07/07/2011 9:49 AM

Yes, you could have. The most practical approach is to match time-current curves for back up protection, and for proper coordination. I do not have IEC reference, but I can send you some manaufactirers' literatur if you wish.

Register to Reply
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#6

Re: MCCB Rating Selection - Incomer - Outgoing Coordination

07/14/2011 1:14 AM
__________________
shamith gambhir, electrical engineer
Register to Reply