On Load Tap Changer

07/07/2011 12:53 PM

what would be the effect of manually operating the on-load tap changer for a 10MA 33/11kV energised power transformer on no load?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#1

Re: ON LOAD TAP CHANGER

07/07/2011 1:10 PM

BZZZT! Oh, you mean with proper personal protective equipment?

Since it has no load, why don't you turn it off and do some preventive maintenance/inspection on the gear? Sounds like a good opportunity.

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#2

Re: ON LOAD TAP CHANGER

07/07/2011 1:53 PM

Manually operating it will change the secondary voltage in the same way it changes for automatic operation, except that the change is initiated by you without it sensing a need to change. That's what the manual control is for. It won't hurt the tap changer - you can even do it on load. It could put the voltage outside of the desired range, though.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Participant

Join Date: Jul 2011
Posts: 4
#4
In reply to #2

Re: ON LOAD TAP CHANGER

07/08/2011 6:12 AM

Thanks for the reply, the OLTC to our transformer was recently faulted during commissioning and I was wondering whether it had everything to do with the fact that it was operated on no load conditions

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: ON LOAD TAP CHANGER

07/08/2011 4:06 AM

Try it, but go down in voltage rather than up and don't go too far. A while ago I had a problem with VFD's failing at the weekend. We tracked the problem down to one of the 20MVA transformers OLTC's drive motor. It had tripped out on overload so at the week end the voltage would rise and destroy the VFD's.

__________________
The reports of my death are greatly exaggerated.