Anonymous Poster #1

CT Reversed

07/09/2011 2:25 PM

What will happen if the polarity of a CT is reversed in one phase by mistake while replacing the same that meant for protection of a power transformer( say 33/3.3KV,4MVA) ?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: CT Reversed

07/10/2011 4:31 AM

Try it and find out.

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2

Re: CT Reversed

07/10/2011 7:29 AM

Most likely the protection will malfunction. However, please download and study this paper : http://www.gedigitalenergy.com/multilin/notes/artsci/art07.pdf

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Member

Join Date: Jul 2011
Posts: 5
#3

Re: CT Reversed

07/12/2011 12:22 AM

you can reversed the S1,S2,or P1,P2.

__________________
Blue Jay Electronic provide high performance power meter, energy meter, and industry automatic solution.
Reply
Member
Engineering Fields - Electrical Engineering - New Member

Join Date: Jan 2011
Posts: 5
#4

Re: CT Reversed

07/12/2011 12:42 AM

When only P1 P2 is reversed, breaker will trip on instanteneous earth fault.

Reply