Conductor Ampacity

07/11/2011 1:01 AM

Are the conductor ampacities specified in the NEC, the actual threshold values for such conductors or were they specified with a certain allowance? What are the real tolerance of such conductors? (say 2% higher that what is specified)? Finally, are there available data as to when a conductor fails?

Register to Reply
Pathfinder Tags: conductor ampadity
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Conductor Ampacity

07/11/2011 3:48 AM

British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Conductor Ampacity

07/11/2011 5:25 AM

Could you be more specific, threshold of what? The conductor getting so hot it destroys the insulation in a cable or the conductor blows like a fuse?

Stick to the recommended ratings given, it's safer!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Conductor Ampacity

07/11/2011 1:03 PM

The tables in the NEC are abundantly clear as the the exact conditions that apply to the ampacity ratings. Take them at face value, there is no such thing as "tolerance" in these regulations. In other words if the table that applies to your installation conditions says that you can safely apply 432A in your conductor, then you cannot run it at 433A.

But make sure you read ALL of the conditions. For instance you must almost always size your cable to handle 125% of the determined load, rounded to the nearest size up. So if you have a 432A load, the cable you select must be rated for at least 520A and if there is a size that is capable of 519A, you must chose the next higher size.

Also, being that you reference to the NEC (National Electric Code), I'll assume you are in the US in which case the British Standard would not apply.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Jun 2008
Posts: 14
#11
In reply to #3

Re: Conductor Ampacity

07/13/2011 12:48 AM

Thanks for your response JRaef.

You seem to be very familiar with the code, so I hope you can answer another question, for non-motor loads, is it ok to base the size of wire on the breaker size, say, I have a 100A breaker, I will size the wire for 101A (for example)? What for motor loads?. Motors loads would have higher breaker capacity for the spike currents but is it ok for the wires to be rated less than the circuit breaker?

Register to Reply
Power-User

Join Date: Apr 2011
Location: Bengaluru, India
Posts: 128
Good Answers: 3
#13
In reply to #11

Re: Conductor Ampacity

07/13/2011 1:08 AM

Basically all equipments have a thermal withstand characteristics. This is usually defined by an equation of the format

[I2] x[ t] = K

Normally this is an inverse characteristic. with infinite time at currents less than continous rating , which reduces inversly when current exceeds rating.

This thermal inverse characteristic should be well above the protection characteristics. 1 Ampere margin may not be sufficient. I would keep about 20 to 25% margin.

The decision of this margin may vary from engineer to engineer depending on their personal experience.

__________________
Dr.Raghunatha Ramaswamy - We discover nothing new other than knowledge
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jun 2008
Posts: 14
#14
In reply to #13

Re: Conductor Ampacity

07/13/2011 5:42 AM

This is much enlightening. Thank you Radhunath7!

Register to Reply
Active Contributor

Join Date: May 2011
Posts: 18
#4

Re: Conductor Ampacity

07/11/2011 10:36 PM

You need to be more specific about your application and intent.

Chap. 3, Table 310.16 of the NEC contains the informaton you need if your application is for 600V or less.

There is a process you must apply to select the current (amps) that is needed and from that process, you can source the conductor from the table.

You never want to know when a conductor is going to give out. You always select overcurrent protection devices to elimate, limit or remove that possibility.

If unsure how to digest this information and the advise given by others, you really need to consult a qualified electrician

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#5

Re: Conductor Ampacity

07/11/2011 11:19 PM

Cable withstand current depends on tripping time when overloaded(Amp) or short circuited(kA),ambient temperature,derating factors,maximum operating temperature of conductor and insulation etc. Consult the cable manufacturer.

__________________
pnaban
Register to Reply
Power-User

Join Date: Apr 2011
Location: Bengaluru, India
Posts: 128
Good Answers: 3
#6

Re: Conductor Ampacity

07/12/2011 3:14 AM

The current carrying capacity of a conductor depends on

1. Allowable temperature rise [based on thermal withstand capability, ambient temperature etc]

2. Permisible voltage drop in case of long conductors

3. Stability of interconnected systems, in case of very long lines [EHV transmission lines for example]

Whichever the above 3 is the least, will determine the current carrying capacity. Most likely this value will be less than the figures provided in the tables for a safe design.

__________________
Dr.Raghunatha Ramaswamy - We discover nothing new other than knowledge
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#7
In reply to #6

Re: Conductor Ampacity

07/12/2011 3:54 AM

With a view of copper saving, loading to maximum possible CCC may be a welcome move.

__________________
pnaban
Register to Reply
Active Contributor

Join Date: Jun 2008
Posts: 14
#12
In reply to #7

Re: Conductor Ampacity

07/13/2011 12:58 AM

Hi PNABAN. I think we shouldn't risk it.

I was leaning more on devicing a set-up which can demontrate, SAFELY, conductor failure. A future project maybe.

Register to Reply
Commentator

Join Date: Jun 2008
Posts: 80
Good Answers: 5
#8

Re: Conductor Ampacity

07/12/2011 7:36 AM

You need to define "threshold values" and "tolerance" better. Generally speaking, 1 amp for 5 seconds for every 42.25 circular mils of copper will not cause permanent damage from overcurrent, annealing etc. You should check your termination torques, as you would after any major fault. The NEC is a rule book for the safe use of electricity. It is not intended for use as a design guide and does not contain basis information for the rules that it provides.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jun 2008
Posts: 14
#10
In reply to #8

Re: Conductor Ampacity

07/13/2011 12:31 AM

Thanks for your response Goodho!

What I meant by threshold and tolerance was, how high a continuous current can you apply to a conductor without any adverse effect and for which a higher value would degrade or cause the conductor to fail. But your response would answer this.

Just wondering, where did you get such value (1A / 42.25CM)?

Register to Reply
Active Contributor

Join Date: Apr 2007
Posts: 22
Good Answers: 1
#9

Re: Conductor Ampacity

07/12/2011 9:55 AM

If you are a member of NFPA, The NFPA offers online webinars that speak directly to applications for your queries. I recommend that you take these online webinars. Knowing where to find ampacities for cables in the NEC is good knowledge. However there are other things to take into account such as in-rush current, voltage drop, distance of cable, types of cable, number of conductors in the raceway, type of raceway, temperature factors, and other design factors that are not really covered from an intergrated design system standpoint in the NEC 2011. These seminars allow you to "put the entire picture together", as a member of NFPA you can take these online webinars at a discount and recieve daily updates of changes in NEC code. Membership is not expensive. The webinars are inexpensive and keep you up to date with industry developements. Mike Holt also offers good courses in these areas and they come in CD sets.

Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

cyoung (1); Gizmo787 (1); Goodho (1); JRaef (1); Louwel (4); pnaban (2); PWSlack (1); raghunath7 (2); TonyS (1)

Previous in Forum: Desigo BMS   Next in Forum: Can it be Used for Charging Lead Acid 12v Battery?

Advertisement