System Fault Current

07/11/2011 6:34 AM

Dear All,

i need small clarification as below,

we have 15MVA(132/11KV) transformer with impedance of 10%. so Fault KA around 10.3KA. in this case why we have to choose 31.5KA inseatd of 10.3KA VCB breaker rating. the problem will be 10.3KA breaker availbality issue or anything else. Kindly suggest me.

regards,

N.Ganesan

__________________
Knowledge Sharing
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: System Fault Current

07/11/2011 8:52 AM

Simply because it's the size on the market. Manufacturer make a standard range, if you want bespoke equipment then you will have to pay for it.

What is the problem with higher rated equipment if it's relatively cheap?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Commentator

Join Date: May 2011
Posts: 84
Good Answers: 1
#2

Re: System Fault Current

07/11/2011 1:46 PM

Dear Ganesan,

Since your so called VCB will be on the bus connected to the transformer. The most imp consideration is Fault MVA and fault current of the bus. Now, this bus must be connected to diff equipments having their own %imp, so hereby increasing the fault current and fault MVA on the bus.

therefore, VCB is selected as per fault KA of the bus. not the equipment connected to it.

Register to Reply
Member

Join Date: Jul 2010
Posts: 9
#3

Re: System Fault Current

07/12/2011 2:43 AM

You do not select circuit breaker switchgear based on the steady state fault level, you must enure its capable of coping with transient fault levels which it may require to break.

Register to Reply
Commentator

Join Date: Jun 2011
Location: Hyderabad, India.
Posts: 92
Good Answers: 2
#4

Re: System Fault Current

07/12/2011 1:59 PM

I want to give a simple method to estimate maximum short circuit current with a 3-phase fault on secondary of the transformer.

Isc( Symmetric Short Circuit Current) = secondary current of the Transformer divided by percentage impedance.

In this case secondary current is 15MVA/(1.732x11KV)= 787.3Amps

Hence Maximum Isc = 787.3/(10/100) = 7.87KA.

I do not know how you got 10.3KA. even if you have big Induction motor connected on the same Bus of transformer.

The best and accurate method is draw the whole network with their per unit impedances. Apply the Thevenin theorem then you will get accurate short circuit current.

Now the question is why to go standard VCB. Custom made VCB will be very costly and needs more time to construct. So it is better to use nearest higher side standard rating of VCB.

__________________
B.E, M.I.E, M.S
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: System Fault Current

07/27/2011 10:13 AM

Yes! Availability is the issue.