This is the first time that I am participating in this forum and I hope that I will learn from your expertise and help me out in sorting the following problem: (Please do not hesitate to correct me if my reasoning is not correct)
The system I am currently working on consists of a parallel configuration of three 800KVA (G1,G2,G3) generators. Duriong operation the active loading (KW) is equally shared amongat the three sets but on the other hand the reactive loading varies tremendously in the range of 70 KVAr for G1,-15 KVAr for G2 and +15 KVAr for G3.
It is evident that the reactive loading is not equally distributed amonst the three.
Note: It is woth pointing out that the load current of G1 is approximately 100Amps higher than G2 and G3.
In a parallel set-up we always try to achieve equal loading in both the active and reactive parts.
It is to my understanding that the current problem i.e. variance in the KVAr is due to improper adjustments in the generators excitation since reactive load is a function of it.
In the caser of generator G2 having a -ve VAr signifies that generator is in an under-excited mode i.e. excitation is decreased below that required to make the generator terminal voltage equal to grid voltage thus G2 is importing Var (and not exporting as it should be)
Although this might be a trivial problem for some of you I would like to clear this out since I am new in this field.
In view of the above problem would you please confirm the following:
1) The unbalance in VAr can it be resolved by adjusting the generators field voltage i.e. excitation (in view of the large discrepancies) and is this accomplished throughthe generators AVR?
2) Is the 100A increase in G1's load current be attributed to this unbalance?
3) Are there any other possible issues that i need to consider in order to resolve
1) the reactive unbalancing
2) the 100A load current discrepancy of G1 as opposed to G2 and G3?
Kind Regards
Ryan