We have 50kA, 1 sec S/C fault current level for transformer of 11/3.3 kV having Dyn11 vector group. The value of NGR is 6.92A. How is this NGR value calculated?
__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
NGR Value (in Ohms) = Phase Voltage of the system / desired earth fault current.
In your case, the desired earth fault current (on the 3.3kV star side, I presume), is decided as 6.92A. Hence, the Ohmic value of the NGR is: 275 Ohms.