How to Calculate NGR?

07/18/2011 7:19 AM

We have 50kA, 1 sec S/C fault current level for transformer of 11/3.3 kV having Dyn11 vector group. The value of NGR is 6.92A. How is this NGR value calculated?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: How to Calculate NGR?

07/18/2011 12:51 PM

I do not believe "The value of NGR is 6.92A". The value of NGR is in ohms. So you can use Ohm's law to calculate the value of the resistor.

I = E/R or R = E/I. Don't forget the calculate the required wattage.

Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2

Re: How to Calculate NGR?

07/19/2011 9:00 AM
__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: How to Calculate NGR?

07/26/2011 11:28 AM

NGR Value (in Ohms) = Phase Voltage of the system / desired earth fault current.

In your case, the desired earth fault current (on the 3.3kV star side, I presume), is decided as 6.92A. Hence, the Ohmic value of the NGR is: 275 Ohms.