The Ohmic value of the NGR is: Phase-to-Neutral Voltage during healthy conditions divided by the desired earth fault current.
The desired earth fault current is the choice of the customer. Better to keep it very low (preferably below 25A) if one wants to avoid core damages in the alternator, but then, detection of an earth fault would be difficult.
Alternately, the desired earth fault current could be kept about 400A; then detection is possible, but then, the chances of generator core damage would be high.
However, the maximum permissible is the three-phase-short-circuit current.
It is always a compromise.
Also, refer to www.i-gard.com; They have some real good publications on NGRs.
There are primarily three types of grounding system which are:
(1) Solid grounding – The neutral point of the system is grounded without any resistance. If the ground fault occurs, high ground current passes through the fault. Its use is very common in low voltage system, where line to neutral voltage is used for single phase loads.
(2) Low Resistance grounding (LRG) - This is used for limiting the ground fault current to minimize the impact of the fault current to the system. In this case, the system trips for the ground fault. In this system, the use of line to neutral (single phase) is prohibited. The ground fault current is limited to in the rage from 25A to 600A.
(3) High Resistance Grounding (HRG) - It is used where service continuity is vital, such as process plant motors. With HRG, the neutral is grounded through a high resistance so that very small current flows to the ground if ground fault occurs. In the case of ground fault of one phase, the faulty phase goes to the ground potential but the system doesn't trip. This system must have a ground fault monitoring system. The use of line to neutral (single phase) is prohibited (NEC, 250.36(3)) in HRG system, however, phase to neutral is used with using the additional transformer having its neutral grounded. When ground fault occurs in HRG system, the monitoring systems gives alarm and the plant operators start the standby motor and stop the faulty one for the maintenance. This way, the process plant is not interrupted. The ground fault current is limited to 10A or less.
There are other two types such as Corner Grounding (for Delta system) and Ungrounded system but they are not commonly used.
Now, return to your question. The important parameter that is missing here is amount of current you would like to limit with the Neutral Grounding Resistor for your system. For LRG, it is 25A to 600A, while for HRG, it is less than 10A. I assumed your system is LRG and you would like to limit it to 200A (one of the common values in use for LRG).
The line to neutral voltage is 11,000/1.732 = 6,350V
The resistance value is 6,350/200 = 31.75 ohm or 32 ohm.
You have to select the resistance so that it can withstand 200A at least for 10 seconds.
Hope, it helps.
- MS
__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
i want to ask all master in this forum about my design, every month i have ground fault in my sistem and the problem is all low voltage damage due this problem like deepsea, deif and other equiptment.
i want to ask
1. should i use NGR ?
2. went i use NGR how to calculate the NGR because went i calculate base on master nascon wrote it not imagin on my mind.