NGR

07/20/2011 1:37 AM

THE SHORT CIRCUIT CURRENT 50KA FOR 1SEC. DO THIS CURRENT VALUE CONSIDERED DURING CALCULATION OF NGR VALUE FOR A TRANSFORMER?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Jul 2011
Posts: 11
#1

Re: NGR

07/20/2011 1:45 AM

I think the current value is used to chose the protector of transformer. 1 sec is a very long time for protection. In high voltage, the trip time may not reach a sine circle.

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: NGR

07/20/2011 12:40 PM

Think about what you are trying to do. Reduce the magnitude of the ground fault. What is the magnitude of the fault you want? Ohm's Law.

http://www.postglover.com/Literature/NG112-06_Tech_Info.pdf

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: NGR

07/26/2011 11:09 AM

NGR Value = Phase Voltage of the system / desired earth fault current. It has nothing to do with the symmetrical fault current such as 50kA, etc.

Register to Reply