Protection for Ungrounded System

07/20/2011 12:39 AM

Just would like to ask for the most reccomended protection for an ungrounded system...or any current sensing devices aside from thermistors built-in in motors..our present system employs multilin from g.e..and we believed that it is already been obsolete...

Reccomendations are highly appreciated....

Thank you..

__________________
take care of your seconds and the minute will take care of itself..
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Jul 2011
Posts: 11
#1

Re: protection for ungrounded system

07/20/2011 1:34 AM

Maybe I hasn't understand your meaning totally.

Firstly, which potentail grade are you using now?

If it is low as 380V ,we still use thermal relay to deal overload and short circuit, residual current device to ground fault.

If it is higher voltage , now we don't use in protector in break, but use computer protect system, which it to collect signals of current and potential then calculation,to check whether there are fault in circuit.

Register to Reply
Anonymous Poster #1
#2

Re: protection for ungrounded system

07/20/2011 2:35 AM

You can add overcurrent protection to your scheme as an earth fault condition is a form of overcurrent as well because it contains positive and negative sequence components with the zero sequence current that will flow. The fault current will therefore be I1+I2+I0 which will be considerably more than normal load current. With carefull calculation and with the right type of relay you will be able to distinguish between phase and earth faults.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: protection for ungrounded system

07/20/2011 3:50 AM

Try reading the Wikipedia article on earthing systems.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#4

Re: Protection for Ungrounded System

07/21/2011 12:14 AM

It sounds to me AGAIN as a basic misunderstanding. Since the original info is so sketchy, let assume delta connected motors. Well, they are protected according to the code. And the only grounding is in the main power panel, again according to the code.

And the code is updated every decade or so. If you are grandfathered, it may or may not be the wisest thing to stick with it..

On the other hand, safety ground from the housing of the tools has to be totally separate, local, and is not expected to carry much current. IF, safety device is in this circuit, it has to trigger at 10 - 20Milliamps depending on local code.

Register to Reply
Power-User

Join Date: Apr 2011
Location: Bengaluru, India
Posts: 128
Good Answers: 3
#5

Re: Protection for Ungrounded System

07/21/2011 1:10 AM

If the system is completely ungrounded, there will not be any ground fault current as there is no path for the same. In this case ground impedance will be infinity. Recall that ground fault currents are minimized by having neutral impedance. A ungrounded system is equivalent to having an infinite neutral impedance.

Earth fault protection will not be necessary , unless there is a possiblity of two simultaneous earth faults to form a closed loop, through the charged circuits.

protection against phase faults, and unbalances will be needed for circuits. Thermal protection for the motors will be needed measuring phase currents and negative sequence currents.

__________________
Dr.Raghunatha Ramaswamy - We discover nothing new other than knowledge
Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Aug 2010
Posts: 111
Good Answers: 2
#6
In reply to #5

Re: Protection for Ungrounded System

07/23/2011 12:09 AM

i find your answer is very related to the question i posted..lastly, do you have any recommendation on the best device to protect our system...

__________________
take care of your seconds and the minute will take care of itself..
Register to Reply
Power-User

Join Date: Apr 2011
Location: Bengaluru, India
Posts: 128
Good Answers: 3
#7
In reply to #6

Re: Protection for Ungrounded System

07/23/2011 12:50 AM

I have not worked with sensitive earth fault protection before. May be the following links will be useful to you

http://www.startco.ca/library/papers/Ground-Fault%20Paper.pdf

__________________
Dr.Raghunatha Ramaswamy - We discover nothing new other than knowledge
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#8

Re: Protection for Ungrounded System

07/26/2011 11:13 AM

What protection are you talking about? Over current or short circuit or earth fault?

Register to Reply
Register to Reply 8 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); electricalexpert65 (1); gritee (1); leveles (1); PWSlack (1); raghunath7 (2); rockraiden (1)

Previous in Forum: Substation Transformer Voltage Sag   Next in Forum: NGR
You might be interested in: DC Motors, Stepper Motors, AC Motors

Advertisement