Anonymous Poster #1

Substation Transformer Voltage Sag

07/19/2011 6:41 PM

Hi,

during a tap change for few mseconds there is a voltage sag in the system. the voltage goes down from 115V to 98V for 8 mileseconds.

we have tested for the winding resistance test using MTO-210 for testing "make befroe break" and this test doesn't show any problem. The SFRA also doesn't show any obvious problem. we tested for excitation, PF, TTR,... no obvious signs. One of the engineers suggestion was that it might be the LTC lead loose/bad connection in the tank, but the test couldn't confirm this.

Is there anyone might have some idea to findout the source of this problem.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: Substation Transformer Voltage Sag

07/19/2011 8:33 PM

Well 8 milliseconds is almost exactly one half cycle of a 60 Hz signal. Unless you really did mean 8 mile seconds? Then with the electricity traveling at a nominal 65% of the speed of light in a vacuum that puts it at about 121,000 miles/second.... Nah that's not making sense. You must mean that you see a power dip for one half of a power cycle. Frankly, I can think of some power distribution arrangements that this would be normal. I can also think of ones that this would be a sign of instability. It all depends on your configuration and your method of testing. Sorry but I don't have enough information to go on.

Or maybe I've just confused myself again.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Anonymous Poster #1
#3
In reply to #1

Re: Substation Transformer Voltage Sag

07/20/2011 9:28 AM

Hi redfred,

not mile seconds, but it is milliseconds. Thanks for the correction. However the exact sister unit feeding the same load doesn't exhibit the voltage sag problem during the tap change transition.

any thought?

Reply
Power-User

Join Date: Jun 2009
Posts: 134
Good Answers: 11
#2

Re: Substation Transformer Voltage Sag

07/20/2011 12:21 AM

Isn't this dip normal for this type tap changer.

Talk to tap changer manufacture.

Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#4
In reply to #2

Re: Substation Transformer Voltage Sag

07/20/2011 4:00 PM

I agree with Carl Pugh, check with the LTC manufacturer.

However, it could be a problem with the contacts of the tap changer. How old is it? How many operations does it show on the op counter? If the contacts are very burned, there could be arcing taking place, or poor contact making/breaking. This could cause voltage excursions. Maybe a tap changer internal inspection and service is required. Contact a reputable, experienced HV testing & maintenance company for help.

__________________
To get the right answers, first you need to ask the right questions.
Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#5

Re: Substation Transformer Voltage Sag

07/20/2011 11:42 PM

Mechanical contacts rarely move in the single Millisec range. 10 msec or above is good. Now, improvements are made with make before break arrangement.

BUT, wherever real power is in play, contacts normally come in pairs. One makes and breaks, suffers from arcing. And for all this abuse, its contact characteristics are not great. The other of the pair is not abused. It only makes contact after the first, to make a low Ohm safe connection.

IF, you cannot measure precise enough to distinguish, and your abused first contact is flaky or already failed, you described your situation quite correctly.

Reply
Guru
United States - Member - Born, raised halfway 'round .....

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#6

Re: Substation Transformer Voltage Sag

07/21/2011 10:49 AM

The slight power sag or delay may have been caused by a contact bounce or some sort of dirt caught in between the contact points?

__________________
vsar
Reply
Anonymous Poster #2
#7

Re: Substation Transformer Voltage Sag

07/26/2011 5:37 PM

Hi there

Check the Tapchanger contacts...maybe they are burnt

Cheers

Reply
Reply to Forum Thread 7 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); Carl Pugh (1); leveles (1); PeterT (1); redfred (1); vsar (1)