Lightning Arrestor Installation

07/25/2011 6:42 AM

Friends, Is it proper to link or loop the Ground pit for Lightning Arrestor to the electrical ground pit of a building through a conductor?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: lightning arrestor installation

07/25/2011 8:24 AM

What does the local code say?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#2

Re: Lightning Arrestor Installation

07/25/2011 2:03 PM

If it isn't connected to the same earthing source, then it doesn't really work as a lighting protection system, does it?

The building would be set at a different potential when a stroke of lightning hits, providing no protection to anything except the protection system!

As stated, the local code will tell you this.

Register to Reply
Commentator

Join Date: Jun 2011
Location: Hyderabad, India.
Posts: 92
Good Answers: 2
#3

Re: Lightning Arrestor Installation

07/25/2011 4:25 PM

NEC Article 250-86. This provision shall not prohibit the required bonding together of grounding electrodes(loop for building grounding & eletrode for lightning protection) of different systems which will limit potential differences between them and between their associated wiring systems.

__________________
B.E, M.I.E, M.S
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: Lightning Arrestor Installation

07/26/2011 10:26 AM

By all means! IS 2309 mandates that the Lightning Protection System must be connected (bonded) to the plant services earthing. Even IEEE 1100, IEC 60364 & the IEEE Green Book prescribe the same.

Register to Reply
Register to Reply 4 comments
Copy to Clipboard

Users who posted comments:

cuba_pete (1); electricalexpert65 (1); Mushtaq Hussainh (1); PWSlack (1)