Loss of Field

07/26/2011 5:00 AM

What is loss of field.How it is tested with the help of kit?

Register to Reply
Pathfinder Tags: loss of field
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: Jul 2010
Posts: 32
#1

Re: Loss of Field

07/26/2011 7:33 AM

To say shortly,Loss of field is disturbed terminal voltage of generator which in turn affects the stability of the system.for more details go through this discussion. It will make you clear. http://www.control.com/thread/1276103698

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Loss of Field

07/26/2011 10:16 AM

When a generator is synchronised to a bus and if during its operation, the generator's excitation system fails, then this generator would draw the reactive power (excitation) from the bus and would deliver active power to the bus (sort of an induction generator). This condition is called loss of field. It is quite dangerous, as the stator current could become 200% of rating, rotor heating, etc.