what is the maximum measureable primary current of the CT 600/1 A
Re: CT RATIO
07/27/2011 6:16 AM
At a guess, 600A.
Re: CT RATIO
07/27/2011 6:46 AM
its very difficult to answer the question.. because you didnt mention about the class of CT, and for which purpose u r going to use this CT..
Re: CT RATIO
07/27/2011 8:22 AM
Neither did the original poster!
Good Answers: 170
Re: CT Ratio
07/27/2011 9:27 AM
That depned supon the Instrument Security Factor (ISF) in case of Mesurement CTs and the Accuracy Limiting Factor (ALF) in case of Protection CTs.
Re: CT Ratio
07/27/2011 1:38 PM
Hi
Your best measureble current of a CT is just before your CT saturation point eg:
A point were the voltage rises by 10% and the current rises by 50%...does that make sence to you...shout if it does not then I try again!!