Burner for Kerosene/Diesel Oil Water Boiler

07/27/2011 7:52 PM

I have a small 300 litres water boiler which runs on Kerosene/Diesel Oil. It is fired manually by putting a flame above the burner provided at the bottom of the boiler. The burner is connected to a two inch GI pipe from the Air Blower with a gate valve and a half inch GI pipe from a 40 litre oil tank through a nozzle valve to control the flow of oil.

When enough temperature is achieved, which takes hardly a minute, the boiler is fired and the flame is regulated by contolling the air and the flow of oil.

Problem comes when Power Supply goes off. The air blower stops and boiler starts smoking.

1. Can I use an Inverter for the blower (170 watt)? Will it take the starting current for the air blower? What capacity (VA) and which make is recommended?

2. Can you suggest a Burner which can control the air/fuel and take care of power breaks simultaneously.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#1

Re: Burner for Kerosene/Diesel Oil Water Boiler

07/27/2011 10:03 PM

Solenoid shut off valve as close to the nozzle as possible. So when power goes off valve closes. Will keep the excess oil from spraying. Which the nozzle has to bleed off from the pump when stopped.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Reply Score 1 for Good Answer
Guru

Join Date: Apr 2007
Location: Buenos Aires, Argentina
Posts: 1679
Good Answers: 33
#2

Re: Burner for Kerosene/Diesel Oil Water Boiler

07/28/2011 12:47 PM

As electricity supply seems to be an issue were the boiler is located, instead of using an inverter and a bank of batteries, I would turn the entire system (blower + electro-valves + controllers) to 12V. Electricity would be supplied by a couple of batteries (with less amps tan required for the inverter). Batteries can be charged directly with a regular charger... provided electricity supply is really an issue requiring more backup, you also can use other sources for 12V generation as solar panels, an aerocharger or even a water turbine. Good Luck in this project!

__________________
the more I move, the deeper I get stuck !
Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#3

Re: Burner for Kerosene/Diesel Oil Water Boiler

07/28/2011 11:02 PM

Oil burners are generally configured as follows.

There is a medium (a few atmospheric pressure) pump to the spray nozzle, which in a conical spray atomizes the oil. There is one or two spark plugs with normally wider gap than in cars, in the path of that spray. As soon as the blower starts, the pump starts and the high voltage transformer starts for the spark plugs. All fed from 50 or 60 Hz power mains. When flame is ignited, an electronic eye (photosensor in an evacuated glass tube) senses it, and the ignition is turned off. The electronic eye keeps sensing the flame. That's it.

Since nobody can guarantee, that ignition occur in the very split second the spraying starts, raw oil will sometimes will be sprayed to the walls. Hence smoking then, or the next time. Treat it as diagnostics, for when something goes really wrong.

Blowers run in the 100-200Watts, Pumps a bit more. Neither has more than 2x for staring current. But how about measuring your own.? An ammeter will do fine.

Reply
Active Contributor
Engineering Fields - Chemical Engineering - New Member

Join Date: Jul 2011
Posts: 17
#4

Re: Burner for Kerosene/Diesel Oil Water Boiler

07/29/2011 1:58 AM

The boiler is a manually fired one.For any boiler for safety reason,during stoppage the fuel should cut first,which is reverse in your case.Other than smoking there is a chance of explossion.

so far I understand your fuel is supplied by either gravity flow or by the pressure in the tank.

Solinoid valve on fuel line is the simplest solution,or you can install a pilot burner which will run on by ambient air.

This is a minimum requrement for safety.

Reply
Member

Join Date: Jul 2011
Posts: 5
#5

Re: Burner for Kerosene/Diesel Oil Water Boiler

07/29/2011 2:32 AM

Try using a portable air compressor as an air blower with the required CFM which will be fuel operated.

Reply
Reply to Forum Thread 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!