Generator Engine Power

07/28/2011 3:49 PM

Hello,

I have question regarding the engine power of our 180kw CAT 3306B generator. When the motor (50Hp) transfer to delta (star-Delta Starter) the engine rpm or Hz drops to below 45Hz and exausted heavy black smoke, untill the motor run steady the engine rpm back to normal. normally the engine rpm drops 1Hz only. Engine HP = 272

Where is the problem is it the Turbocharger or Injector nozzle?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#1

Re: Generator Engine Power

07/28/2011 3:58 PM

Could be one or more injector nozzles, the turbo charger, bad fuel, worn engine, clogged air filter, ect.

Is the gen-set still under warranty?

Can the dealer you purchased it from (assumed) suggest a competent diesel mechanic to diagnose the problem?

Has anything changed on the load end? More equipment, higher than usual load?

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
Active Contributor

Join Date: May 2011
Posts: 20
#2
In reply to #1

Re: Generator Engine Power

07/28/2011 4:16 PM

The Engine is an old one no warranty, they told me mechanic had it overhauled , but this engine was not working for nearly 2 years sometime after overhauled due to electrical problem on the Alternator. Its working now 50hr after alternator was repaired for now it is use for welding works and test motor on bansaw (40"). The Filters are new fuel are clean, so maybe its either injector nozzles, or turbocharger.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Dec 2010
Location: 1° North Singapore
Posts: 568
Good Answers: 17
#3

Re: Generator Engine Power

07/28/2011 6:51 PM

When diesel engine emits heavy black smoke, it means incomplete combustion due to lack of air, check your engine air inlet ,air filter , that is the first thing to do.

__________________
Sharing knowledge is one thing that defies basic arithmetic logic --- the more you share, the more you get!
Register to Reply
Power-User

Join Date: Sep 2006
Location: Houston Texas
Posts: 282
Good Answers: 16
#4

Re: Generator Engine Power

07/28/2011 10:38 PM

Check also that the engine is up to temperature before applying power. Low cylinder temperature will also cause incomplete combustion and black smoke.

__________________
Specializing in Dynamic Weighing Systems for Powder and Bulk Solids Handling
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#5

Re: Generator Engine Power

07/28/2011 11:07 PM

Is this a new problem?. Was it running earlier without trouble?. Is it possible to start the motor without load and later apply load?.Check the engine as well as connections and contacts in the starter including "rolling" of phases. If nothing works try with a suitably rated capacitor across the starter only during starting.

__________________
pnaban
Register to Reply
Guru

Join Date: Jun 2009
Location: Ontario Canada
Posts: 930
Good Answers: 31
#6

Re: Generator Engine Power

07/29/2011 9:11 AM

When your engine labors the governor opens the fuel rack to allow more fuel to overcome the load. At this time if you do not have sufficient air you will get black smoke.You may have an indicator on the air intake that if working properly shows red when the air filter is restricted a preset amount. Also check intake hoses for collapsing and restricting air. If you have a turbocharger check it for wear and possibly take an intake pressure reading with a 0-60 pis or equivalent pressure gauge. Compare reading to specs. Several checks should be taken from start up to full warm up. What are the amps when under load , you can pull more amps than the engine can overcome. If all this checks out look for a plugged or partial plugged exhaust system.. Not common on Cat but frequent of Deutz Diesel.

__________________
The fine line between cuddling and holding one down to prevent escape must be learned
Register to Reply
Power-User

Join Date: Jan 2007
Location: Johannesburg, South Africa
Posts: 230
Good Answers: 16
#7

Re: Generator Engine Power

08/03/2011 2:32 PM

I recall my one contractor some time ago using a 180 or 200kW motor to power a large fan with a 150kVA motor in a tunnel ventilation application. Usually, they had to overspeed the engine slightly before switching on the fan, as otherwise it would just belch some black smoke and die. The engine was not capable of sustaining the high power requirement during start-up. They eventually went for a larger engine - problem solved.3

Register to Reply