Side Bands in FFT Spectrum of Faulty Motor's Current Signature

08/04/2011 3:17 AM

Hi, I'm working on fault detection of motors through "motor current signature analysis". FFT of the input current drawn from motor is taken and analyzed. For a healthy motor there should be just one peak in the FFT spectrum, i.e at the fundemental frequency at which the motor is operation(FIGURE 1). On the other hand, if the motor is faulty then there will be an additional pair of "side" peaks at frequencies equidistant from the main fundemental frequency.(FIGURE 2).

(FIGURE 1)

(FIGURE 2)

Now for different faults in the induction motor, the occurence of these frequencies will be at different frequencies. Here is where my question comes. That why certain faults correspond to side frequency peaks at a certain point and not anywhere else!!

Your help would be highly appreciated! Also please tell me which forum should i post this question at?

Regards,

Danish

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Associate

Join Date: May 2011
Posts: 46
#1

Re: Side bands in fft spectrum of faulty motor's current signature

08/04/2011 3:19 AM

FIGURE 1

Register to Reply
Guru

Join Date: Dec 2010
Location: 1° North Singapore
Posts: 568
Good Answers: 17
#2

Re: Side bands in fft spectrum of faulty motor's current signature

08/04/2011 6:27 AM

Normally FFT spectrum gives you a spectrum of harmonics which are multiple of fundamental frequency. But the harmonic you show in about 75 Hz, which is not the harmonic. Are you sure you capture the correct spectrum?

It certainly does not look like it.

Also, I am curious about motor current signature analysis. Do you have examples of what kind of motor fault give what kind of pattern of spectrum ?

__________________
Sharing knowledge is one thing that defies basic arithmetic logic --- the more you share, the more you get!
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Side bands in fft spectrum of faulty motor's current signature

08/04/2011 8:17 AM

The first analysis shows peaks at f/2 and 3f/2 at about -40dB. These are not coming from the motor. They are distortion from somewhere on the power system upstream.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Dec 2010
Location: 1° North Singapore
Posts: 568
Good Answers: 17
#4
In reply to #3

Re: Side bands in fft spectrum of faulty motor's current signature

08/04/2011 8:25 AM

No matter how you distort , you will not get half harmonic, the FFT spectrum will only give frequecies in multiple of fundamental. The OP's spectrum is something else.

__________________
Sharing knowledge is one thing that defies basic arithmetic logic --- the more you share, the more you get!
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: Side bands in fft spectrum of faulty motor's current signature

08/04/2011 10:33 AM

Quite.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
3
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#9
In reply to #3

Re: Side bands in fft spectrum of faulty motor's current signature

08/04/2011 10:49 PM

I would not discount that spectrum too fast.

If the motor is connected on a gearbox or a pulley with un-even loading around the rotation, you could get these fluctuations in current.

It might also applies to a bent shaft or a ceasing bearing.

What about a off round stator caused by incorrect mounting or dropping of the motor.

Now, if you want an interesting spectrum, connect it to an old VFD that switched at low frequency and had some DC offset on the outputs...

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply Good Answer (Score 3)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#6

Re: Side Bands in FFT Spectrum of Faulty Motor's Current Signature

08/04/2011 11:54 AM

There are a few things that must be clarified to proceed.

  • What type of AC motor is this; induction motor, universal motor, synchronous motor, single phase, three phase?
  • What type of motor failure condition exists that makes this waveform; stalled rotor, shorted stator pole winding, open stator pole winding, shorted or open rotor winding (universal motor)?
  • What is the rotor rotational speed during this fault condition?
  • You've shown us the FFT current amplitude values. What difference do you see in the FFT current phase analysis signals?
__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Anonymous Poster #1
#7

Re: Side Bands in FFT Spectrum of Faulty Motor's Current Signature

08/04/2011 5:20 PM

I like PWSlack's answer. Bravo, could you maybe explain in a little more slow person friendly terms :P. Specifically how you know what the fundamental frequency and/or the harmonic is.

Register to Reply
Guru

Join Date: Dec 2010
Location: 1° North Singapore
Posts: 568
Good Answers: 17
#8
In reply to #7

Re: Side Bands in FFT Spectrum of Faulty Motor's Current Signature

08/04/2011 6:11 PM

The OP already said about the fundamental frequency. In any case ,it is either 50 or 60 Hz, the spectrum diagram shows 50 Hz. I thought this is obvious.

__________________
Sharing knowledge is one thing that defies basic arithmetic logic --- the more you share, the more you get!
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#10

Re: Side Bands in FFT Spectrum of Faulty Motor's Current Signature

08/05/2011 12:06 AM

Power lines are quite dirty in any office / manufacturing site. I am not believing any reading without solid proof that it is not coming from the power line from inside or even outside of the site!

He has his work cut out to convince himself, THEN us on that account. Labs and test rooms cost a bundle for a reason!

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#11
In reply to #10

Re: Side Bands in FFT Spectrum of Faulty Motor's Current Signature

08/05/2011 12:36 AM

I agree. With a nearly 60db side lobe to main lobe difference I would expect that this is actually an artifact of the power main voltages. A simultaneous comparison of the supply voltage and motor current will settle that. I still say that a comparison of the AC current phase to the AC voltage phase will be more informative than the amplitude. Now what might be real useful is to take the raw LabView data and find the amplitude of the real power drawn by the motor. That should show some interesting effects as the rotor gets loaded or a winding phase opens.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Associate

Join Date: May 2011
Posts: 46
#12

Re: Side Bands in FFT Spectrum of Faulty Motor's Current Signature

08/08/2011 1:37 AM

Thank you for all your comments!

Firstly the two images that i've shown are reference signals taken be a PHD thesis of motor current signature analysis! I just want to know that why do the side bands even occur at various frequencies due to different faults?? For example first sideband peaks due to broken rotor bars occur according to this formula

Fb = (1± 2s) fL

where Fb is the side band frequencies, s= slip of the motor and FL is the line(supply) frequency.

So the question is that why does it follow this formula everytime for broken bar faults??.. why always at twice the slip frequencies?

Are there any physical explanations to this??. i couldnt find any answers on the internet. So looking upto you people to help me out!

Thanks once again for your replies

Register to Reply
2
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#14
In reply to #12

Re: Side Bands in FFT Spectrum of Faulty Motor's Current Signature

08/11/2011 8:00 AM

Full-load slip for an induction motor is about 0.02 to 0.03 of synchronous speed. So 2s rotor bar fault would give frequencies about 50 +/- 2.5 Hz - not +/- 25Hz. I suggest you get 2s because, for an individual phase; the faulty bar is at the "top" stator pole, then the "bottom" pole during one revolution of rotor. Remember that stator windings are in pairs, one each side of the rotor. That makes two "bumps" in one slip cycle.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#13

Re: Side Bands in FFT Spectrum of Faulty Motor's Current Signature

08/11/2011 7:00 AM

The levels at 25 & 75 Hz are -60 dB compared to fundamental current. That is 1 millionth the fundamental power lost in a series resistance - is that enough to regard as a fault? As has been noted, you have not given evidence that these are not in the input voltage or due to 25 Hz and its harmonics - rather than sidebands. And if it were a 1500 rev/min motor rotating at half the supply rate, components at 25Hz, 75 Hz would be no surprise. More clarity on the motor speed, if the motor is normal or faulty and a spectrum say 20 to 200 Hz are needed.

Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

67model (2); Anonymous Poster (1); bravo88 (3); danishrizvi (2); leveles (1); marcot (1); PWSlack (2); redfred (2)

Previous in Forum: Drum Level Control   Next in Forum: Type of Digital Input Cable for PLC/DCS

Advertisement