Anonymous Poster #1

Prevention of Generator Shutdown Due to Fault

08/04/2011 9:09 AM

We have a problem on our system due to the shutdown of generator sets whenever a downstream fault occurs on our feeder.

We have 3 units of generator, 2 260 kva and 1 163kva, all of which has a voltage rating of 480 volts output supplying 2 units of 400kva and 1 unit 225kva step up transformer with voltage rating of 480/13200 volts.. This supplies a lone feeder of 3 phase primary lines extending over some kilometers. When a downstream fault occurs on any part of the system, a generator shutdown follows which incurs a total power outage to the the coverage area.

The type of protection and sectionalizing device use all through out are fuse cut outs with type K fuse links from Chance. How will we be able to extinguish faults downstream without it reaching the generator preventing total power outage?

Thanks!

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: PREVENTION OF GENERATOR SHUTDOWN DUE TO FAULT

08/04/2011 9:15 AM

Please explain how generation of 683kVA is supposed to support a load of 1025kVA.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster #1
#2
In reply to #1

Re: PREVENTION OF GENERATOR SHUTDOWN DUE TO FAULT

08/04/2011 9:22 AM

the load is only reaching a peak demand of 350kv.. and only 2 units are being used in the operation for some time and then the other unit is turned on to make one unit rest. this is the cycle of the operation on our distribution system. only 2 units are generating at a time.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: PREVENTION OF GENERATOR SHUTDOWN DUE TO FAULT

08/04/2011 9:27 AM

What is the nature of the fault?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster #1
#4
In reply to #3

Re: PREVENTION OF GENERATOR SHUTDOWN DUE TO FAULT

08/04/2011 9:35 AM

for example a single line to ground fault, a double line to ground fault and a line to line fault, this makes the generator sets shutdown. is there a way to extinguish the fault without the fault current reaching the generator sets?

by the way during faults, our fuse cut outs are down. but still the the generatos sets shut down. is there any type of fuse links which are acting faster than type K of AB Chance?

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: PREVENTION OF GENERATOR SHUTDOWN DUE TO FAULT

08/04/2011 9:43 AM

Line to ground faults can be disconnected using residual current circuit breakers, which have been discussed in these columns any number of times before. Their job is to disconnect the fault when one occurs downstream of them, like any other protective device. With good system design, only the affected part of the system will shut off, leaving other users powered and the generators running.

A line-to-line fault is best cured by having overload circuit breakers, correctly sized and selected, that discriminate between the minimum current needed to disconnect the faulty circuit and the maximum current needed to trip the generation off. Once operated, the faulty circuit is disconnected safely leaving other users supplied with power and the generation still running.

It sounds as though investment in a system review and follow-up recommendations by a qualified Electrical Engineering Consultant locally would be money well spent. Basically, hire someone who can look at it and sort it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster #1
#7
In reply to #5

Re: PREVENTION OF GENERATOR SHUTDOWN DUE TO FAULT

08/04/2011 9:59 AM

thank you sir. actually, i have known this idea before but we can't still afford to provide such protection system.. in our urban areas, we provide such expensive protection system. but this problem we have is in our remote areas where power transformers are still not available to supply power.

i just wanted to know if there are better ways to suppress this problem or any how to prevent it with the use of less expensive protection such as fuse cut outs.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #7

Re: PREVENTION OF GENERATOR SHUTDOWN DUE TO FAULT

08/04/2011 10:06 AM

"Can't afford"?

Whatever happened to "can't afford not to"?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster #1
#14
In reply to #11

Re: PREVENTION OF GENERATOR SHUTDOWN DUE TO FAULT

08/04/2011 10:11 AM

yes sir. it's not easy for our small distribution to purchase this. i am working with a non profit utility that is why.

Reply Off Topic (Score 4)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#20
In reply to #14

Re: PREVENTION OF GENERATOR SHUTDOWN DUE TO FAULT

08/04/2011 10:30 AM

Then look at loss of revenue from customers due to faults, and the investment needed to avoid them. Go for cases that show an easy payback.

Not-for-profit doesn't mean no-investment.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#25
In reply to #20

Re: PREVENTION OF GENERATOR SHUTDOWN DUE TO FAULT

08/04/2011 10:49 AM

Oops. Easy pay-back first. The initial savings made then pay for the longer-to-pay-back investments.

With investment money so cheap in these low-interest-rates times, generating business cases (pardon the pun) for investments is so easy.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#6
In reply to #1

Re: PREVENTION OF GENERATOR SHUTDOWN DUE TO FAULT

08/04/2011 9:49 AM

You're assuming that the transformer load rating is the whole circuit load rating. Now it might be the actual anticipated total load. If it is then there's nothing that can be done. For whenever the total load gets connected, the generator protection system will hopefully prevent the generators from being damaged.

Now if the total load is actually less than the available power from this generator set then the circuit breakers (fuses) can be sized to be less than what the transformers can support (if full power was available). This way a real fault will have the breaker as the weakest link instead of the generator protection system.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Anonymous Poster #1
#8
In reply to #6

Re: PREVENTION OF GENERATOR SHUTDOWN DUE TO FAULT

08/04/2011 10:03 AM

thank you sir. but i cant get into your idea.

i just wanted to know if there is anything i could do to solve this problem?

Reply Off Topic (Score 4)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #8

Re: PREVENTION OF GENERATOR SHUTDOWN DUE TO FAULT

08/04/2011 10:06 AM

Eh? That is the solution.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #6

Re: PREVENTION OF GENERATOR SHUTDOWN DUE TO FAULT

08/04/2011 10:07 AM

Indeed. Until the OP explained it no other question could be asked.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#16
In reply to #12

Re: PREVENTION OF GENERATOR SHUTDOWN DUE TO FAULT

08/04/2011 10:14 AM

My initial reply got interrupted so I did not see your exchange with the AP with the added information.

It never ceases to amaze me how the cost of protection systems are frequently considered to be too expensive.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Off Topic (Score 4)
Anonymous Poster #1
#18
In reply to #12

Re: PREVENTION OF GENERATOR SHUTDOWN DUE TO FAULT

08/04/2011 10:17 AM

thank you so much sir for your time

Reply Off Topic (Score 5)
Anonymous Poster #2
#9

Re: Prevention of Generator Shutdown Due to Fault

08/04/2011 10:04 AM

I feel the time taken by fuses to isolate will be too long and that might be causing the generators to trip due to overload before the fuse melts.

Shouldn't you go for the faster isolators - relay+ breakers?

Reply
Anonymous Poster #1
#13
In reply to #9

Re: Prevention of Generator Shutdown Due to Fault

08/04/2011 10:08 AM

i guess you were pointing out same idea as with sir PWSLACK. can there be any more unexpensive ideas?

Reply
Anonymous Poster #2
#17
In reply to #13

Re: Prevention of Generator Shutdown Due to Fault

08/04/2011 10:15 AM

Yeah, Sorry PWS, the credit goes to you. .

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#23
In reply to #17

Re: Prevention of Generator Shutdown Due to Fault

08/04/2011 10:45 AM

CR4, is a team effort, AP2!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#26
In reply to #13

Re: Prevention of Generator Shutdown Due to Fault

08/04/2011 11:36 AM

What is the cost of not doing it (rhetorical question)?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster #2
#15
In reply to #9

Re: Prevention of Generator Shutdown Due to Fault

08/04/2011 10:13 AM

On second thought -

You may have faults at generating station (and its wiring/ bus upto transformers)

Individual transformers

Single transmission line

Distribution points.

If it is anywhere in the transmission line, assuming it is not on ring loop, then how does it really matter whether your generator works or not?

Even in your single line-earth fault or line-line fault, you can not isolate the faulty phase and let other phase run in a 3 phase generator. So even if everything is protected by as I mentioned, your system can not be switched on till the fault is rectified.

If it is a ring loop of course then you should have sufficient number of breakers, strategically placed to isolate the faulty section. But then I am not sure about your configuration.

Reply
Anonymous Poster #1
#32
In reply to #15

Re: Prevention of Generator Shutdown Due to Fault

08/06/2011 10:02 AM

sir, i guess your comment is way off what i wanted to know.

thanks anyway

Reply Off Topic (Score 5)
2
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#19

Re: Prevention of Generator Shutdown Due to Fault

08/04/2011 10:22 AM

Why not install downstream fusing with a slightly lower fault threshold than the shutdown threshold of the gen-set?

IMO, in theory the fuse should drop before the gen-set shuts down.

Inexpensive - maybe worth a try.

__________________
The first 5 days after a weekend are always the hardest................................
Reply Good Answer (Score 2)
Anonymous Poster #1
#21
In reply to #19

Re: Prevention of Generator Shutdown Due to Fault

08/04/2011 10:36 AM

yes i guess thats it. finally..

i think we have a problem on fuse sizing. we have a coordinated fusing system but i guess its the fuse rating that we are having problem with

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#22
In reply to #21

Re: Prevention of Generator Shutdown Due to Fault

08/04/2011 10:44 AM

That's why a fresh pair of (qualified) eyes is needed.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster #1
#24
In reply to #22

Re: Prevention of Generator Shutdown Due to Fault

08/04/2011 10:46 AM

indeed sir. anyway, sir PWSLACK, where you from sir?

Reply Off Topic (Score 5)
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#27

Re: Prevention of Generator Shutdown Due to Fault

08/04/2011 12:09 PM

One thing I didn't see is what form of protection is tripping the gen-sets. There may be an opportunity to make this relaying less sensitive to long distance faults by making sure that the relaying is properly tuned. If everything is ok then the next step is to consider the use of a distance relay, an inverse current vs time relay or a combination of both, the idea being to discriminate between a generator or close in bus fault. If this is too expensive then consider increasing the trip time delay or adding a simple time delay relay in the generator trip circuit (at the risk of not acting fast enough if there is a legitimate generator, transformer, or close-in fault).

If you can provide more info on what's tripping the generator it would help all of us see the true nature of your problem.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#28
In reply to #27

Re: Prevention of Generator Shutdown Due to Fault

08/04/2011 1:57 PM

Good grief! That would be far too expensive!

I think we're on a chewing gum and a bit of string budget here. Any expense spared.

__________________
The reports of my death are greatly exaggerated.
Reply
Anonymous Poster #1
#33
In reply to #28

Re: Prevention of Generator Shutdown Due to Fault

08/06/2011 10:08 AM

yes sir you're right

Reply Off Topic (Score 5)
Anonymous Poster #1
#31
In reply to #27

Re: Prevention of Generator Shutdown Due to Fault

08/06/2011 9:53 AM

thank you sir for the comment. the genset shuts down during faults. its built in circuit breaker is enable during this condition. the circuit breaker is set to the full load rating of the generator

Reply
Power-User

Join Date: Apr 2011
Location: Bengaluru, India
Posts: 128
Good Answers: 3
#29

Re: Prevention of Generator Shutdown Due to Fault

08/05/2011 1:01 AM

This is a protection and coordination problem. Your generator side protective devices must have a time discrimination in operation with respect to the load side protective device.

Though the transformer ratings are larger, than combined generator rating, there may not be any problem due to this.

Consider using relays instead of fuse. I am afraid, unlike relays fuse may not reset its operation.

__________________
Dr.Raghunatha Ramaswamy - We discover nothing new other than knowledge
Reply
Anonymous Poster #1
#34
In reply to #29

Re: Prevention of Generator Shutdown Due to Fault

08/06/2011 10:29 AM

sir, your solution is too expensive.. maybe you haven't read some of the comments added on this discussion

Reply Off Topic (Score 5)
Active Contributor

Join Date: Jun 2011
Posts: 13
#30

Re: Prevention of Generator Shutdown Due to Fault

08/05/2011 9:10 AM

you should provide single line protection drawing. after that only your question can be answered

Reply
Reply to Forum Thread 34 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (16); KJK/USA (1); PWSlack (11); raghunath7 (1); RAMConsult (1); redfred (2); subhash wad (1); TonyS (1)

Previous in Forum: Power Loss/Pole of 16A MCB   Next in Forum: solid state voltage stabiliser

Advertisement