HFD Circuit Breaker

08/04/2011 1:01 PM

Hi guys,does any body have an ideas about under what condition the designer would use HFD CB?

OR what is the difference between HFD CB and other types?

thanks

Register to Reply
Pathfinder Tags: power distribution
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: HFD Circuit Breaker

08/04/2011 3:21 PM

HFD appears to be nothing more than a series designation for a model of circuit breaker by Cutler Hammer (Westinghouse).

Best you have a look at the datasheets.

Is this a customer request to supply this particular circuit breaker? If so they have most likely specd it as their prefered circuit breaker on site or in their equipment (this makes maintainence and holding spare parts on site of replacement easier if there are few part variations on site).

__________________
jack of all trades
Register to Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: HFD Circuit Breaker

08/05/2011 4:45 AM

"HFD appears to be nothing more than a series designation for a model of circuit breaker by Cutler Hammer (Westinghouse)."

Actually, Siemens (US) uses the same designations for the old ITE breakers, but they mean different things.

In Siemens / ITE, the "F" means it is a 250A frame size, the D is manufacturing series, i.e. it is newer than the "C" series of breakers they stopped selling 30+ years ago. In Cutler-Hammer / Westinghouse, the "F" is the Series (age) of breaker, in other words it is older than the current "G" line of breakers, the D means it is a 150A frame.

But in BOTH cases, the "H" in the front happens to mean the same thing; High interrupting capacity. So in C-H / West., the FD is rated 25kAIC, the HFD is rated 65kAIC. In Siemens / ITE, the FD is rated 35kAIC and the HFD is rated 65kAIC.

So a designer would select a High interrupting breaker if they know that the Available Fault Current (AFC) in the system they will be connected to is greater than the next lowest rated breaker. In other words if you were applying this breaker to a system with 38,000A AFC, you cannot use the FD in either brand, you must use the HFD.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)