Anonymous Poster #1

Interference

08/09/2011 5:45 AM

I have a small query, we are run the Power Cable tray (440V) TO Instrumentation Signal (4-30mA) Cable Tray with a distance of the trays 100mm any interference between them

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Interference

08/09/2011 5:57 AM

4-20mA is an industry standard signal that is largely immune to interference. It was chosen as a standard as a result of its immunity to interference.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Active Contributor

Join Date: Aug 2011
Location: Hyderabad
Posts: 14
#2
In reply to #1

Re: Interference

08/09/2011 6:11 AM

Yes Sir,

O.K, what is my query is

Power Cable tray and Instrument Signal (4-20)mA 24V d.c Cable trays are run on parallel (Side by Side) im my recent project. As per Site Conditions available Space is only 50 to 100mm. Any interference shall be occured between Power and Signal Cables. Please Explain me briefly and inform if any standard applicable.

Thanks & Regards,

Srinivas.

Reply Off Topic (Score 5)
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3
In reply to #2

Re: Interference

08/09/2011 10:19 PM

I am assuming you are using shielded pair for the instrument signal cable and multi-conductor (not single conductor) for power cable.

NEC doesn't have restriction of using same tray for multi-conductor power cable and instrument cable (see NEC 392.9 A), but with having a solid fixed barrier between lower voltage rated cable (< 600V) and higher voltage rated cable (> 600V) (see NEC 392.6 F).

However, in the specifications of many projects, power cable and instrument cables are suggested to run in separate trays. NFPA 79 has a guideline to have 15" - 30" distance between power cable and instrument cable at different criteria (I don't have much detail at this moment).

I would suggest you to look into the project specification. If the specification doesn't have anything restriction about the minimum distance for the electrical and instrument trays, yours 100mm distance should be fine.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply Score 1 for Good Answer
Active Contributor

Join Date: Aug 2011
Location: Hyderabad
Posts: 14
#5
In reply to #3

Re: Interference

08/11/2011 5:19 AM

Thanks for giving a valueble information, it is very usefull to me.

Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #2

Re: Interference

08/10/2011 4:27 AM

The signal cablke is unlikely to interfere with the power cable, and vice versa. That is the reason for the current signal being designated a standard in the first place (as already indicated in #1).

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Off Topic (Score 5)
Associate
New Zealand - Member - New Member

Join Date: Aug 2007
Location: Christchurch, New Zealand
Posts: 39
Good Answers: 1
#6

Re: Interference

08/13/2011 7:33 PM

One of the sources of interference is cross coupling between cables. Cable separtation will reduce this considerably. 100mm will certainly have a major effect, but it depends on the magnitude of the interfering signal and the sensitivity of the equipment.

There is another source of interference, especially when VFDs are used. This is conducted noise which will spread through all the metalwork that is bonded together and to earth.

The best way to correct this, is to install the VFD correctly. This requires as low a high frequency impedance between the motor frame and the VFD frame.

Typically, this is achieved by the use of a screened cable correctly bonded to the frame of the VFD and to the frame of the motor.

For more information, see http://www.vfd-emc.co.nz

Reply
Reply to Forum Thread 6 comments