Surge Protection/Lightning Protection for VFD's

08/09/2011 7:43 PM

A plant's electric load of VFD is +95%

Surge protection/lightning protection is required. These are 3 phase VFDs therefore +95% of the loads are three phase. The decision was made to make the system a 3 phase 3 wire based on this fact.

How can you utilize SPD/TVSS that work in this system voltage configuration?

The literature i have explored on SPD and TVSS from Square D point out that a solidly grounded system is a must to use this equipment. Is that true for all SPD/TVSS devices?

If there is no alternative but to make the system solidly grounded to accommodate for SPD/TVSS what are the pros and cons of making this change?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Participant

Join Date: Aug 2011
Posts: 4
#1

Re: Surge Protection/Lightning Protection for VFD's

08/09/2011 10:22 PM

Have you looked at total protection solutions? This data sheet shows 3 -wire Delta systems with ground. http://www.tpssurge.com/st-series/st400-tps.pdf

I assume you have a ground. You don't need a neutral leg just a solid ground.

The guys at Technicon can help you get the unit you need.

Reply
Anonymous Poster #1
#2
In reply to #1

Re: Surge Protection/Lightning Protection for VFD's

08/10/2011 12:03 PM

you are correct. There is a ground.

I will read your references.

thanks!

Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#3

Re: Surge Protection/Lightning Protection for VFD's

08/10/2011 11:40 PM

The literature i have explored on SPD and TVSS from Square D point out that a solidly grounded system is a must to use this equipment. Is that true for all SPD/TVSS devices?

Yes.. or it doesn't work!