MVA Method of Short Circuit Calculation

08/10/2011 2:06 PM

To the experts in electrical design,

i would like to consult you regarding the calculation of system short circuit using MVA method. Do the standby generator contribute to 415 bus short circuit when it is only use during the failure of a 2 MVA, 6.6/0.415 , 6% transformer? the generator have a capacity of 1500KVA, 415 volts. it will automatically run when no 415 volts supply coming from transformer and connected to 415 bus thru ATS, It will automatically off and disconnected to 415 bus when trnasformer power resume. the load of the 415 volts bus are induction motors. My analysis it should be computed separately but when i checked some sample in google they include the generator in fault contribution to the bus.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: MVA Method of Short Circuit Calculation

08/10/2011 2:55 PM

My analysis it should be computed separately independently, as in do your own homework

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: MVA Method of Short Circuit Calculation

08/10/2011 3:14 PM

My analysis it should be computed separately but when i checked some sample in google they include the generator in fault contribution to the bus.

Funny that, being you are trying to calculate the short circuit current. Also funny when you consider that a downstream fault should operate the protection before the transformer changes over to to the generator hence the backup generator in parallel with the transformer won't be trying to feed the same short circuit the transformer was (which is pointless), regardless of the changeover scheme employed for the standby generator.

This really sounds like a homework question rather than a practical application in the real world.

__________________
jack of all trades
Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3

Re: MVA Method of Short Circuit Calculation

08/10/2011 6:59 PM

Since the generator is connected to the utility power with the ATS (Automatic Transfer Switch), there is no possibility that the generator will run in parallel with the utility. In this case, you have to compute the short circuit separately. Out of the two separate studies, you need to consider the highest short circuit current value for the system design. However, if there is any possibility that the generator will run in parallel with the utility, you need to do the single study with both sources.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply
Associate

Join Date: Nov 2009
Posts: 42
#4
In reply to #3

Re: MVA Method of Short Circuit Calculation

08/11/2011 2:45 AM

Thanks a lot Sir. Their is no chance that transformer & generator will run in parallel because of safety features installed both software & electro-mechanical . Now i have support of my theory to my boss.