i have the undervoltage relay X2U-AC from woodward containing various settings e.g. trip voltage and trip time delay . there are dipswitches for settings the value of a parameter called hysterisis which can be set to 3% or 6% or 10% . now what does this parameter mean , what are its affects on network and to which value should i set it ?
Good Answers: 804
Re: undervoltage relay settings
08/10/2011 11:59 AM
Hysterisis in this context would be the difference between the trip threshold and the reset threshold. So let's say it is a 400V system and you want to trip off at 350V. If you set the hysterisis for 10%, you will be unable to reset it until the voltage returns to at least 385V (350 x 1.10). This prevents rapid cycling of the system.
What you set the UV trip threshold is an engineering function that involves investigating the voltage tolerances of the equipment being fed by this system.
India - Member - New Member
Good Answers: 164
08/10/2011 12:10 PM
GA
i admire your patience in replying well despite the questionable history of the OP !
Good Answers: 804
08/10/2011 12:29 PM
It was for the greater good (although I'm not as sure of the assessment of the OP as others are, kind hearted curmudgeon that I am sometimes). Other people read these threads when they do a keyword search, acrimony* will have no value to them.
( * Although I hasten to admit my share of acrimony in this forum as well, I am trying to be kinder and gentler...)
Good Answers: 164
08/10/2011 1:06 PM
You are right about the 'collateral benefit'. i am an example am i not ? So, keep it up ... more power to you.....