Power Transformer

08/11/2011 6:39 AM

why use an additional low voltage bushing for power transformer 60/10kv

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: Aug 2011
Location: India
Posts: 29
Good Answers: 2
#1

Re: Power Transformer

08/12/2011 1:16 PM

My interpretation is as below, though more info. needed for the trafo:

Power trafo 60/10 kV -

60kV HV side, 10kV LV side

Why use an additional LV bushing -

Considering LV (10kV) side is wye connected, neutral star point is brought out through Additional LV Bushing for mounting of neutral CT/neutral grounding.