Anti Motoring protection of steam generator

08/11/2011 11:45 AM

I know that the reverse Power Relay is used to prevent the motoring of large powered steam generator in case turbine trips due to mechanical failures. Should this condition trip the generator excitaion system also?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: Anti Motoring protection of steam generator

08/11/2011 10:39 PM

Generally speaking, yes. Why would you want to keep the field energized since the turbine trip should have already taken the entire unit off-line.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jun 2011
Posts: 13
#2
In reply to #1

Re: Anti Motoring protection of steam generator

08/15/2011 8:27 AM

I was wondering whether no load excitation would be a better option than no excitation. What if mechanical trips are of transient nature?

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3
In reply to #2

Re: Anti Motoring protection of steam generator

08/15/2011 10:56 PM

It's a matter of control/operational philosophy. Something caused the trip to occur, therefore most operators would want to know why. If you are getting nuisance trips and you immediately try to resynchronize without regard for the cause then be my guest. If your trip closes the steam and/or fuel supply valves then it will be some time before you will be ready to resynchronize, and resetting the excitation system will be the quickest item in your startup checklist.

But the number one reason to not keep the excitation on the field is overheating of the generator iron due to overexcitation (the Volts per Hertz problem) and reduced cooling as the speed drops. From ABB... http://www.abb.com/product/db0003db004281/c12573e700330419c1256e77002fb8f5.aspx "...Overvoltage, underfrequency, or a combination of the two can result in excessive flux density in the generator or transformer iron, producing heat that can reach damaging levels. Heating damage to the transformer or generator, if severe enough, can result in costly equipment outages..." It's your call.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jun 2011
Posts: 13
#4
In reply to #3

Re: Anti Motoring protection of steam generator

08/16/2011 1:40 PM

Thanks for discussion and answers.