Cable Tray

08/11/2011 11:32 AM

Hi guys,

IS IT OK TO RUN 120V CABLES ALONG WITH 600V CABLES WITHIN THE SAME CABLE TRAY???

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#1

Re: CABLE TRAY

08/11/2011 11:47 AM

You are running into HV and LV issues there. You need to check with you national and local requirements/code for guidance.

Register to Reply
Active Contributor

Join Date: Aug 2011
Posts: 12
#3
In reply to #1

Re: CABLE TRAY

08/11/2011 12:37 PM

both issues are LV !

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#5
In reply to #3

Re: CABLE TRAY

08/11/2011 2:29 PM

Sorry. In DoD 600V is the cutoff for what is considered HV. I was referring to interior wiring.

Register to Reply
Anonymous Poster #1
#2

Re: CABLE TRAY

08/11/2011 12:25 PM

There are different guidelines that you have to study (eg fill area, supports etc) however NEC does allow 600V or less cables to be routed through the same tray so for you, though on the border, it is still OK.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: CABLE TRAY

08/11/2011 1:38 PM
__________________
The reports of my death are greatly exaggerated.
Register to Reply
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#6

Re: CABLE TRAY

08/11/2011 6:35 PM

Per NEC, it is allowed. Here is the quote from NEC:

392.6 (E): "Multiconductor cables rated 600 volts or less shall be permitted to be installed in the same cable tray".

392.6 (F)(2): "The cables rated over 600 volts are separated from the cables rated 600 volts or less by a solid fixed barrier of a material compatible with the cable tray".

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#7
In reply to #6

Re: CABLE TRAY

08/11/2011 6:51 PM

thanks, GA

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#8

Re: Cable Tray

08/17/2011 10:12 AM

Yes! As long as you maintain a clearance of at least 300mm between the two cables.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#9

Re: Cable Tray

08/17/2011 12:17 PM

<Assuming here that you are in the US because you are referencing 120VAC>

IIRC, the NEC will require that all of them must have the same insulation level and at the highest voltage in the tray / raceway. So when you run the 120V circuits, you must use wire that says 600V (or more) on the insulation. Most of the time that will be the case, i.e. THHN or THWN etc, but some appliance wire and "bell wire" is only rated for 300V, you cannot use that if it's in the same tray. The exception (sort of) is multi-conductor signal cables, but even then the outer jacket must be rated for the highest voltage in the tray. If you use conductors that say "TC" or "Tray Rated", that will have a 600V jacket.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10

Re: Cable Tray

12/22/2022 4:26 AM

Only if Caps Lock is turned off first.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 10 comments